Old 12-09-2012, 10:14 AM   #1
Two circuits on one 2-pole breaker
I was looking at my service panel and discovered that a single 2 pole 20A breaker is being used to provide power to both a 120 v load (using a neutral) and and 240 v load without a neutral). The combined load is less than 10 amps. Is this arrangement permitted by the NEC?
czars is offline   Reply With Quote
Old 12-09-2012, 10:29 AM   #2
A "Handy Husband"
rjniles's Avatar
Yes, you have a MWBC (Multi Wire Branch Circuit) with line to line (240) and line to neutral (120) load.
Coastal South Carolina
rjniles is offline   Reply With Quote
Old 12-09-2012, 10:33 AM   #3
E2 Electrician
stickboy1375's Avatar
Yes, done all the time, I generally do it when an air handler is 240v and I need a 120v receptacle located at the unit as well.
Old 12-09-2012, 10:38 AM   #4
JOATMON
ddawg16's Avatar
I like that......that way if you kill power to ether ckt....your killing both....better than have your 121 power from a different breaker.
Common Sense is like Deodorant. Those that need it the most don't use it.
My
and
ddawg16 is online now   Reply With Quote
Old 12-09-2012, 12:09 PM   #5
A "Handy Husband"
rjniles's Avatar
I am not sure I would like that. You turn off the air handler and you lose power to the receptacle for lights and tools.
Unless you use a disconnect for the air handler only.
Old 12-09-2012, 12:47 PM   #6
E2 Electrician
Of course a disconnect is at the AHU... and besides, money is always an issue, so that's what they get.
Old 12-09-2012, 12:48 PM   #7
E2 Electrician
Nope.... and I really don't care... Money is time, and time is money.
Panel Question concerning 3 pole breaker Shinerbalk Electrical 39 07-21-2012 12:33 PM
Main Power Breaker at Service Pole Trip Continually dens1 Electrical 15 11-26-2011 10:04 AM
2 pole breaker waynebo Electrical 2 06-05-2011 12:36 PM
short circuit. reset the breaker, but no power bp91708 Electrical 10 03-18-2011 11:07 AM
Dual Pole Breaker Amperage Question jcwilshire Electrical 2 11-22-2010 01:45 PM