czars 12-09-2012 09:14 AM
I was looking at my service panel and discovered that a single 2 pole 20A breaker is being used to provide power to both a 120 v load (using a neutral) and and 240 v load without a neutral). The combined load is less than 10 amps. Is this arrangement permitted by the NEC?
rjniles 12-09-2012 09:29 AM
Yes, you have a MWBC (Multi Wire Branch Circuit) with line to line (240) and line to neutral (120) load.
stickboy1375 12-09-2012 09:33 AM
12 Attachment(s)
Yes, done all the time, I generally do it when an air handler is 240v and I need a 120v receptacle located at the unit as well.
ddawg16 12-09-2012 09:38 AM
I like that......that way if you kill power to ether ckt....your killing both....better than have your 121 power from a different breaker.
rjniles 12-09-2012 11:09 AM
I am not sure I would like that. You turn off the air handler and you lose power to the receptacle for lights and tools.
Unless you use a disconnect for the air handler only.
stickboy1375 12-09-2012 11:47 AM
12 Attachment(s)
Of course a disconnect is at the AHU... and besides, money is always an issue, so that's what they get.
stickboy1375 12-09-2012 11:48 AM
12 Attachment(s)
Nope.... and I really don't care... Money is time, and time is money.