First off, as you will soon see, I am not an electrician. I was having a discussion with a friend of mine about wire gage and capacity. If you twist the ends of say two #10 coated wires does that give you more voltage capacity that just one wire? Would it be advisable to do that if that was the wire you had available? Say you wanted to install a 30 amp circuit that was a 150 ft run and only had #10 wire.
Calrob77 is offline   Reply With Quote
Old 06-07-2012, 01:41 PM   #2
Rewards Points: 6,652
150feet 30amp, would work on #10. No problem about that short of length. It would even work with #12. The only thing that you did not state was the voltage. As for twisting, no it would not be needed, or something that you would want to do. They do do what you are stating for speaker wiring, but in turn, does not improve anything.
Old 06-07-2012, 01:49 PM   #3
joed's Avatar
Rewards Points: 12,016
If you are talking about amps and not volts then using two #10 wires would allow more amps to be used. However the electrical code does not permitted using two wires in this fashion unless they are larger than #6.
Old 06-07-2012, 02:13 PM   #4
Appreciate the info.
Old 06-07-2012, 02:15 PM   #5
Thanks. I thought that 150 feet would be too long of a run for #10 for 30 amp.
Old 06-07-2012, 04:40 PM   #6
Semi-Pro Electro-Geek
Rewards Points: 2,902
Voltage rating depends only on the insulation of the wire, not the gauge or number of wires in parallel.
mpoulton is offline   Reply With Quote
Old 06-07-2012, 05:14 PM   #7
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
1/0 AWG is the smallest size wire allowable by code to parallel.... 310.4
The Following User Says Thank You to stickboy1375 For This Useful Post:
brric (06-07-2012)
Old 06-07-2012, 05:15 PM   #8
E2 Electrician
It depends on the actual load.... it may or may not be.
Old 06-07-2012, 06:27 PM   #9
With properly bolted or wirenutted connections at each end you should get almost half the voltage drop at any given current that you would get with a single #10, and the wires won't get as hot as a single conductor because you have more total surface area.
With imperfect connections your parallel arrangement will act like a single #10.
You can test this with a heavy load and voltmeter using an extension cord as a test lead.
The thing is, the smaller the wires used, the less important the connection integrity becomes, so I don't understand the NEC's reasoning in this case.
Old 06-07-2012, 06:39 PM   #10
E2 Electrician
If the wires are not the same exact length is one issue....
Old 06-07-2012, 07:09 PM   #11
That is some really good information. I guess the question now is it alright to go 150 feet with #10 for 30 amps or should he maybe go with a 20 amp?
Old 06-07-2012, 07:18 PM   #12
E2 Electrician
It all depends on the load.... and the maximum voltage drop you want to maintain.
If you want to go 150' and supply a full 30 amps at 120volts with a 5% voltage drop, you would need to run #6 AWG....
As a side note, the breaker stays the same, you only increase wire size to eliminate voltage drop.
Old 06-07-2012, 07:26 PM   #13
Good to know, thanks.
Old 06-07-2012, 07:29 PM   #14
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,142
Regardless this arrangement is prohibited by code.
Coastal South Carolina
rjniles is offline   Reply With Quote
The Following User Says Thank You to rjniles For This Useful Post:
Jim Port (06-08-2012)
Old 06-07-2012, 08:18 PM   #15
Idiot Emeritus
Rewards Points: 1,492
joed is from Canada; it may very well be different up there.
But yes, 1/0 is the smallest size allowed to be run in parallel in the USA.
micromind is offline   Reply With Quote
HVAC Low Voltage Wire raleighthings HVAC 13 12-19-2011 09:08 PM
Changing Two Gang Outlet to Three Gang Outlet vbullinger Electrical 9 01-10-2011 06:13 PM
Dogs chewed my low voltage wire smithlive HVAC 8 06-25-2009 02:44 PM
how to wire a low voltage thermostat to a baseboard heater db3iii HVAC 4 06-05-2009 09:03 PM
Bury Low Voltage Wire in Wall? Tool Junkie Electrical 3 06-16-2008 08:38 AM