Trying To Determine What Size Hacr Circuit Breaker I Need - Electrical - DIY Chatroom Home Improvement Forum
Old 07-21-2012, 06:10 PM   #1
Question
Trying to determine what size hacr circuit breaker I need
I have a newly installed Goodman condenser with a new e coil inside the air handler box as well. This house was built in late 2000 here in Sioux Falls, S.D. I am under the impression they use the National Electric Code from what the city inspector was saying.
I would've uploaded a Photo of the label but I think my photo is to large from what I saw when looking at the info on the photo page.
The specs for the compressor/condenser unit outside are as follows,
A.C.Volts 208-230
Phase 1
Hz
Voltage Range Min 197 Max 253
Max Fuse Amps or Max Circuit Breaker 30
(Time Delay Fuse or HACR Circuit Breaker Required)
Min Circuit Amps 17.6
Fan Motor FLA 0.7 H.P. 1/8
Compressor RLA 13.5 LRA 58.3
Max Working Pressure (No Value Here)
Factory Charge OZ. R-410A 76
Factory Test Pressure Low 240 High 450
This is all that is on the label,
The inspector did say something about being within a certain % of the HACR rating. He wasn't very helpful when I asked him questions as he was more concerned about other things I guess.
A answer would be helpful but a reference of where I can find this information, how to do the calculation would also be good as well as I'm always trying to learn. Some of these numbers don't make sense so anyone that can make sense of them for me I gladly accept your feedback.
My guess is a 30 amp circuit but I only have a 20 in there right now as the wire is only 12 gauge. Its hollowed tubing that the wire can be pulled through is necessary if I need to go to 10gauge.
The only reason I took this job on is the electricians would've been another 3 days and I just got my AC back on this am and it was down since Wed am and we need to get the house cooled down. Ive added regular house circuits but that was years ago using a little cheap hand guide from Menards back in 03 and I cant find that book.
Being that its AC I believe theres a little more to it so I want to be sure. The AC guy said their electricians put 25amp circuit breakers in all the time but with 12 gauge I was always under the impression that 2 was the max limit?
Any and all help is appreciated, Thanks, DN
dtnel is offline   Reply With Quote
Old 07-21-2012, 06:35 PM   #2
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
You could use a 25 or up to a 30 amp. The #12 wire is fine as you have met the minimum circuit ampacity of 17.6 amps
Rules are different when applied to motors
wirenut1110 is offline   Reply With Quote
The Following User Says Thank You to wirenut1110 For This Useful Post:
andrew79 (07-21-2012)
Old 07-21-2012, 07:38 PM   #3
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
You are fine with what you have installed.
12's on a 20A breaker. The HACR part is a rating of the breaker. The breaker must be HACR rated.
Old 07-21-2012, 08:17 PM   #4
Rewards Points: 510
Right, I was pointing out that if he had a problem with the breaker tripping, he could go up to a 30 without having to change the wire size.
Old 07-21-2012, 08:44 PM   #5
kbsparky's Avatar
#12 wire on a 30 Amp breaker. All within specs and Code.
-KB
Old 07-21-2012, 08:47 PM   #6
k_buz's Avatar
I agree with both of you, I was simply pointing out that he is perfectly within the limits of what the AC requires with 12's and a 20A breaker.
Old 07-22-2012, 09:41 AM   #7
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
You could run # 14 AWG and install a 30 AMP breaker if you wanted.
Old 07-22-2012, 11:56 AM   #8
Julius793's Avatar
um how do you figure? romex?
Electricity will kill you if you give it a chance
Julius793 is offline   Reply With Quote
Old 07-22-2012, 12:01 PM   #9
E2 Electrician
#14AWG is good for 20 amps, meets the criteria of 17.6 Min. Circuit Ampacity,
The 30 amp breaker is the largest breaker allowed as stated on the Nameplate.
Old 07-22-2012, 12:03 PM   #10
Julius793's Avatar
not good for 20a romex and thats how most houses are wired.
Old 07-22-2012, 12:05 PM   #11
E2 Electrician
prove me wrong.
Old 07-22-2012, 12:05 PM   #12
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
#14 romex is rate for 15A under the 2011 NEC. 20A under 2008 (for motors, HVAC and everything else listed in 240.4(G)). The OP stated that #12 is already installed which is fine. He can go as high as a 30A breaker depending on if the disco is fused or non-fused.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 07-22-2012, 12:10 PM   #13
Julius793's Avatar
prove me wrong.
get a code book and start reading!!!
Old 07-22-2012, 12:12 PM   #14
E2 Electrician
Im all set, thanks.
Old 07-22-2012, 12:16 PM   #15
E2 Electrician
Im on the 2005 NEC, so I can still use #14 AWG at 20 amps under 240.4(G), but seriously, they change it in 2011 with no data that it is an issue...
Can a Square D 4 pole circuit breaker be used as a 2 pole circuit breaker. TifcoJim Electrical 3 08-24-2011 12:59 AM
New circuit breaker owen22 Electrical 14 01-12-2010 08:08 PM
Replacing a circuit breaker tertius Electrical 9 09-24-2009 09:17 PM
What size breaker for 4100 watt wall oven? romexican Electrical 3 09-15-2009 10:34 PM
Transformer Help chcustom Electrical 28 12-10-2007 11:40 PM