I just bought a dryer (20A, 240V) and a 3-prong cord to match the outlet on my house (which I installed on the appliance). I then plugged it to the 3-prong outlet, but the appliance does not turn on. I checked the breaker box and for the 'dryer' two 20A breakers are assigned.
What should I check for being wrong?
alx11 is offline   Reply With Quote
Old 01-02-2010, 04:37 PM   #2
" Euro " electrician
frenchelectrican's Avatar
Are you sure you have 120/240 volt 30 amp circuit for electrique dryer ???
Typically with 3 wire dryer receptale it will be crowfoot format as I will show you the photo of it. This may look little big but very clear how it hook up
This is typical 3 wire dryer receptale { 30 amp size }
Merci,Marc
Old 01-02-2010, 04:58 PM   #3
What is the Mfg of the dryer ?
Model number ?
What is the plate reading on the dryer for amps/watts ?
STand alone dryer Or combined w/washer ?
Old 01-02-2010, 11:00 PM   #4
Inspector/Instructor
codeone's Avatar
If you have a typical dryer like Marc is showing the neutral and the ground strap in the dryer are not connected. Today the NEC requires Dryers and Ranges to be 4 wire and the grounded (neutral) conductor and ground seperate. With older homes with a 3 wire the ground wire serves as the grounded (neutral) conductor.
If this is the case with your new dryer you dont have a grounded (neutral) conductor for your control cirturity to work.
codeone is offline   Reply With Quote
Old 01-03-2010, 12:49 AM   #5
Licensed Electrician
Magnettica's Avatar
Rewards Points: 150
Send a message via Yahoo to Magnettica
I agree with that!
Union County, NJ, Licensed Electrician
Classic Electric, LLC, Rahway, New Jersey
Magnettica is offline   Reply With Quote
Old 01-03-2010, 10:06 AM   #6
Licensed Pro
The three wire set up is two hots and a neutral... the appliance case is (was) allowed to be grounded to the neutral. If the ground strap is not connected to the neutral, it will have no effect on the appliance operation, but the case will not be grounded.
alx11: You need to check for proper voltage at the receptacle... you should have 240V between the two hots as Marc illustrated.
Old 01-03-2010, 12:22 PM   #7
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
depending on how the pigtail was hooked up to the dryer, he may have connected to the ground and not the neutral. It would be unusual to see but I can imagine it happening.
so, at the dryer, the ground and the neutral must be bonded together due to it being a 3 wire hook up.
if this is a brand new dryer, there should be directions in the manual as to how the pigtail needs to be attached in either a 3 wire or 4 wire connection.
Dryer vent ponch37300 General DIY Discussions 10 01-21-2009 05:26 PM
moisture in dryer vent and door monkeygirl Electrical 13 01-10-2009 10:11 AM
Preparing to install Kerdi on bathtub surround DIY-Renovator Flooring 18 07-17-2008 11:42 AM
Installing dryer outlet in laundry room ManMythLegend Electrical 11 07-13-2008 11:36 AM