Transfer Switch for furnace - rating?
Hi;
I am considering installing a transfer switch for my gas fired furnace to be powered by my portable generator.
I found this one: http://www.homedepot.com/p/Reliance-...6#.Uj426D9p6Uk, and this one: http://www.homedepot.com/p/Generac-1...1#.Uj44XT9p6Uk.
Both list generator running power rating.
My generator power rating (5500 Watts) is well above the rating of either of these switches. Why do they state max power rating for the generator if there is a 15A circuit breaker in the unit?
While I understand that the internal components of the switch may have a maximum rating, I would think that the circuit breaker would protect the unit in case it is overloaded. I intend this device to be used only for the furnace, which draws no more than 5A (including circulation pump). The generator has two 20A circuit breakers to protect its output.
Also, what are code considerations for such an install? I can install the switch at the SE panel or at the furnace, although installing at the SE would eliminate the need to run a cord across the basement floor.
Thanks for your advice.
FW
KE2KB is offline   Reply With Quote
Old 09-22-2013, 08:21 AM   #2
joed's Avatar
The maximum rating is the maximum amount of power that will pass through the switch.
Do not PM with questions that can be asked in a forum. I will not respond.
Old 09-22-2013, 08:35 AM   #3
So, if I install a switch rated for 1500W which will be connected to a generator that can supply 5500W I will fail code inspection?
Is the inspector going to ask to look at the generator?
FW
Old 09-22-2013, 09:09 AM   #4
FW
what type of generator do you have? i presume it has receptacles on it of various amperage ratings. to use these switches, you'll plug an extension cord between your generator and the transfer switch when you lose utility power. while the output of your generator may be 5500 W, it will only output the power required for the load served. i suspect your furnace is on a 15 amp circuit so use a 15 amp output on your generator and you should be fine.
itsnotrequired is offline   Reply With Quote
Old 09-22-2013, 10:13 AM   #5
Electrical Contractor
Philly Master's Avatar
Hi;
FW
Yes that will pass inspection and either will work for the furnace "only"
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
Old 09-22-2013, 10:17 AM   #6
now that being said it would not be the best chioce IMHO ...
something like this would be better ...
if you plan to have "other" things on at the same time ...
it comes in a kit gives you the 30 amp cord, outside box so the gen is outside and away from windows and doors, lots of spaces ( breakers ) and then you can wire up what you want to have ,,,, can turn off what you want or turn it on based on the needs at the time ...
Old 09-22-2013, 11:30 AM   #7
The generator is a Westinghouse WH5500. It has two 20A breakers for the 4 receptacles on the unit (2 on each leg), plus a 4-wire receptacle for 220V or split 220/120V.
FW
Old 09-22-2013, 11:40 AM   #8
I agree. That would be the best way to go. It's only the cost that will be the deciding factor. I am not the one who would pay for the unit; it is my dad, and trying to convince him this is worth the $500 the entire install would cost (probably more with the permit fee) is the most difficult task. But at least I could do the work myself, and that would save plenty!
FW
Old 09-22-2013, 01:59 PM   #9
That kit is about 400.0
Old 09-22-2013, 08:59 PM   #10
Yes, I looked it up on HD and Amazon. I wouldn't need 16 circuits though; I think 10 would be more than enough.
FW
Old 09-23-2013, 04:42 AM   #11
comes with 10 to get 16 you take breakers out and replace them with twins ... the thing we like about it is that it is very easy to reconfigure ...to what is in any particular house ...
Old 09-23-2013, 06:24 PM   #12
E2 Electrician
stickboy1375's Avatar
Generac is crap, just buy a interlock kit to fit your panel.... $200 bucks tops...
Old 09-23-2013, 06:25 PM   #13
E2 Electrician
Seriously? Not every panel can be swapped out with twins....
Old 09-23-2013, 06:39 PM   #14
PLUS the CORD ...PLUS the outside Box
seriously ... i mean really ...since i was ONY talking about ONE panel ...the generac panel it most certianly can .....take TWINS ....
Old 09-23-2013, 06:42 PM   #15
E2 Electrician
You're a generac dealer... keep the kool-aid to yourself....
Transfer Switch Question tom855 Electrical 9 03-19-2013 10:33 AM
Transfer switch question. Adster Electrical 25 03-02-2013 08:42 PM
Hookup..Generator transfer switch to main & sub panel Dick461 Electrical 8 11-05-2012 02:09 PM
Changing A Double Switch to a single pole switch and a dimmer switch loydbrahn Electrical 0 11-08-2011 11:00 PM
fan/light switch buzzing mjlocat Electrical 4 05-23-2010 02:44 PM
Copyright © 2003-2014 Escalate Media. All Rights Reserved.