Top Plate Bore Too Full? - Electrical - DIY Chatroom Home Improvement Forum
Old 06-08-2013, 01:14 AM   #1
Rewards Points: 24
top plate bore too full?
Hello. I have five 14-2 romex from attic going down a top plate bore that is fairly full. I know it's not code. One cable is the incoming power going down to a jbox, feeding the four, that is going up to various devices. It'll have intermittent load, maximum of 117.7 watts. There is a gfci outlet there that I'm using to shut all four cables. A vaccum might get plugged into it once a while. Worst case scenario, I can replace it with a plain gfci only.
Do I have to worry about over heating?
Would removing the outlet make it acceptable?
If making another bore is the only solution, first bore 2 wires, second 3 wires?
TIA
darkomega69
darkomega69 is offline   Reply With Quote
Old 06-08-2013, 01:49 AM   #2
Rewards Points: 332
How do you know it's not to code?
I had a panel moved and the electrician ran more than 5 cables through the bore and it passed inspection.
sgip2000 is offline   Reply With Quote
Old 06-08-2013, 01:53 AM   #3
Rewards Points: 24
I saw a posts a while back and remembered thinking that mine is not to code....like i said....the bore is full......correct me if I'm wrong....Thanks!
Old 06-08-2013, 05:42 AM   #4
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
2 cables per hole ... so 2 new holes .... 2008 and up
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
Old 06-08-2013, 07:30 AM   #5
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,824
Well......this is only a fraction of what this says and is quite misleading
You can have up to FOUR #14, #12 or #10 CABLES in a hole before you need to consider derating. There is NO explicit limit on number of cables.
The point is to keep the number of current carrying conductors to under 10. After that you need to derate these cables to below their "normal" capacity.
I can post all the relevant codes but I don't feel like it right now.
The Following 3 Users Say Thank You to Speedy Petey For This Useful Post:
jbfan (06-09-2013), Jim Port (06-09-2013), Philly Master (06-08-2013)
Old 06-08-2013, 08:02 AM   #6
Rewards Points: 516
something had changed and we are not allowed to put more than 2 cable per hole ..... not sure where it comes from ...but PITA ....blah blah 2 foot rule 7 or less doesn't count .... blah blah
Old 06-08-2013, 08:47 AM   #7
The NEC added the part about more than two NM cables through a hole that is to be fire stopped must be derated. They just refer you to the standard derating chart.
Maybe the two cable limit is a local thing for you?
The Following User Says Thank You to Speedy Petey For This Useful Post:
stickboy1375 (06-08-2013)
Old 06-08-2013, 09:40 AM   #8
Rewards Points: 516
well a top plate would need to be fire stopped .....and then every 4' horozontallly
Old 06-08-2013, 02:05 PM   #9
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Sounds like bull**** to me... someone just mis reading the NEC.
The Following 3 Users Say Thank You to stickboy1375 For This Useful Post:
Jim Port (06-09-2013), sirsparksalot (06-08-2013), Speedy Petey (06-09-2013)
Old 06-09-2013, 01:49 AM   #10
Rewards Points: 24
thanks guys. just fixed it. first hole was to close to wall though...hahaha...drywall repair time. thanks again.
The Following User Says Thank You to darkomega69 For This Useful Post:
Philly Master (06-09-2013)
HELP PLEASE replacing rotted sole, top and bottom plate dolson Remodeling 4 04-16-2010 07:54 PM
Replacing Section of Sole Plate RM575 Carpentry 3 03-28-2010 10:31 AM
Double sole plate how-to? HooKooDooKu Building & Construction 19 03-24-2010 02:43 AM
The case of the hanging base plate KaiserS Building & Construction 4 02-02-2008 07:42 PM
Basement 2x2 furring strips, basement clutter, top plate not attached to floor joists touchsuhas Remodeling 5 12-26-2007 07:01 PM