Tips On How I Can Get This Electrical Job Done For A Hot Tub In Backyard. - Electrical - Page 3 - DIY Chatroom Home Improvement Forum
Old 08-24-2010, 04:11 PM   #31
The Mfgs generally do not address all code issues
Some of them can't even get the code right where they do address it
The one I bought does not mention a grounding grid
I know its required when there is concrete around the tub in the US
This due to the wet concrete forming a grounding path
You step out of the tub....one foot in..one foot on the wet concrete
Zap...you just completed a circuit
Not sure how often it might happen...but may only take once to kill you
Old 08-24-2010, 04:19 PM   #32
Rewards Points: 33
Is this the same for dirt? Say the hot tub is sitting on top of patio slabs ( 24x24), but around that all there is is grass. Would bonding be necessary?
Say I want for safety do the bonding regardless if i need it or not. Where exactly do i bond that lug to?
the punisher is offline   Reply With Quote
Old 08-24-2010, 05:11 PM   #33
Its acgtually kind of involved on what you need to do
Includes pavers:
(A) Performance. Equipotential bonding is intended to reduce voltage gradients in the area around permanently installed pools, outdoor spas, or outdoor hot tubs by the use of a common bonding grid in accordance with 680.26(B) and (C).
(B) Bonded Parts. The parts of a permanently installed pool, outdoor spa, or outdoor hot tub listed in (B)(1) through (B)(7) shall be bonded together with a solid copper conductor not smaller than 8 AWG with listed pressure connectors, terminal bars, exothermic welding, or other listed means [250.8(A)]. Equipotential bonding is not required to extend to or be attached to any panelboard, service equipment, or grounding electrode.
(1) Conductive Pool, Outdoor Spa, and Outdoor Hot Tub Shells.
(a) Structural Reinforcing Steel. Unencapsulated structural reinforcing steel secured together by steel tie wires is considered bonded.
(2) Perimeter Surfaces. An equipotential bonding grid shall extend 3 ft horizontally beyond the inside walls of a pool, outdoor spa, or outdoor hot tub, including unpaved, paved, and poured concrete surfaces. The bonding grid shall comply with (a) or (b) and be attached to the conductive pool reinforcing steel at a minimum of four points uniformly spaced around the perimeter of the walls of a pool, outdoor spa, or outdoor hot tub.
(a) Structural Reinforcing Steel. Structural reinforcing steel [680.26(B)(1)(a)]. Authorís Comment: The 2008 NEC does not provide any guidance on the installation requirements for structural reinforcing steel when used as a perimeter equipotential bonding grid.
(b) Alternate Means. Equipotential bonding conductor meeting the following:
(1) 8 AWG bare solid copper bonding conductor.
(2) The bonding conductor shall follow the contour of the perimeter surface.
(3) Listed splicing devices.
(4) Bonding conductor shall be 18 to 24 in. from the inside walls of the pool.
(5) Bonding conductor shall be secured within or under the perimeter surface 4 to 6 in. below the subgrade.
(3) Metallic Components. Metallic parts of the pool, outdoor spa, or outdoor hot tub structure shall be bonded to the equipotential grid.
(4) Underwater Metal Forming Shells. Metal forming shells and mounting brackets for luminaires and speakers shall be bonded to the equipotential grid.
(5) Metal Fittings. Metal fittings sized 4 in. and larger that penetrate into the pool, outdoor spa, or outdoor hot tub structure, such as ladders and handrails shall be bonded to the equipotential grid.
(6) Electrical Equipment. Metal parts of electrical equipment associated with the pool, outdoor spa, or outdoor hot tub water circulating system, such as water heaters, pump motors, and metal parts of pool covers shall be bonded to the equipotential grid. (see Figure)
Exception: Metal parts of listed equipment incorporating an approved system of double insulation is not required to be bonded to the equipotential grid.
(a) Double-Insulated Water Pump Motors. Where a double-insulated water-pump motor is installed, a solid 8 AWG copper conductor from the bonding grid shall be provided for a replacement motor.
(b) Pool Water Heaters. Pool water heaters shall be grounded and bonded in accordance with equipment instructions.
(7) Metal Wiring Methods and Equipment. Metal-sheathed cables and raceways, metal piping, and all fixed metal parts shall be bonded to the equipotential grid.
Exception No. 1: Where separated from the pool, outdoor spa, or outdoor hot tub structure by a permanent barrier.
Exception No. 2: Where located more than 5 ft horizontally of the inside walls of the pool, outdoor spa, or outdoor hot tub structure.
Exception No. 3: Where located more than 12 ft measured vertically above the maximum water level.
(C) Pool Water. A minimum conductive surface area of 9 sq in. shall be installed in contact with the pool, outdoor spa, or outdoor hot tub structure water. This water bond is permitted to consist of metal parts that are bonded in 680.26(B). Author's Comment: This section was completely rewritten to clarify equipotential bonding requirements for permanently installed pool, outdoor spa, or outdoor hot tub areas.
Old 08-24-2010, 05:45 PM   #34
Rewards Points: 33
So I have to buy a bonding grid and install it underground around the hot tub? And then bond to that ?
The tub is in a corner. One side has concrete and the other side where the steps are is grass. Under the tub is patio slabs.
Not sure what I am suppose to do here. Both electrictians that came out mentioned running wires but nothing about having to install a bonding grid. Where do I buy the bonding grids. ?
Old 08-24-2010, 06:08 PM   #35
Sorry, thats all I know
My last tub was installed in 2004
And its off a wood deck, nothing to bond
Changing from Electrical Cook Top to Electrical Range EkS Electrical 24 06-22-2010 10:43 AM
How to install new electrical box without attic access gilmores33 Electrical 10 02-14-2010 07:46 PM
Electrical Codes and Tips ponch37300 Electrical 51 08-28-2009 10:14 PM
Electrical box replace,addiitions, city permits and looking for an electrician ramchy Electrical 3 08-02-2009 11:12 AM
Outdoor backyard electrical for lighting, water fountain, shed nabz Electrical 1 05-25-2009 09:58 PM