Old 09-05-2012, 03:23 AM   #1
Buzzy's Avatar
Location: The third planet from the Sun; N41◦ 8' 28.446", W73◦ 15' 48.7974"
THWN wire; Gray pvc Conduit; and GFCI receptacles
Hello- I am in need of some help. I am in the midst of installing two exterior lamp posts and two receptacles. My intent is to run the two lamp fixtures on one 15-amp circuit using 14-2 (plus ground) wire; and a separate 20-amp circuit for the two receptacles using 12-2 (plus ground) wire. The run is less than 100'. I'm not concerned about the voltage drop.
I've trenched down 18" and placed the 3/4" gray PVC piping in position. I Went to my local home improvement center to buy the wire. I understand that there are some wires that have what seems to be a dual rating: THHN (high heat resistant) and THWN (heat & water resistant).
The particular brand that is in stock is the SIMpull romex type NM-B for indoor applications; manufactured by the South Wire Co.; it is obviously not rated for wet locations- I verified this at their web site- the wire is a THHN rated wire; contrary to what the clerk working in the electrical department of the home improvement center said. He recommended that I could still use the wires by stripping the outer sheathing and running the wires through the conduit.
My first question is, should I trek over to an electrical supply house and buy the single solid strand of THWN of each gauge wire (by color, e.g black, white, & green) to be code compliant?
Does the ground wire have to be coated or can it lay bare in the conduit? (Remember, if I follow the store clerk's instructions- predicated that his wire was THWN rated, I would be sleeving a bare copper wire through the conduit- where condensation will build up at the very least.)
RE: the receptacles, should they both be GFCIs (exterior rated, of course)?
Thanks in advance! ~Buzzy
Buzzy is offline   Reply With Quote
Old 09-05-2012, 05:17 AM   #2
JOATMON
ddawg16's Avatar
Welcome to DIY...
First off....you don't want to be pulling any type of romex through conduit.....while it can be done, it's not easy and sort of defeats the purpose of the conduit....especially 100'.
Get some THWN stranded wire (all 3 colors) and pull that through the conduit. The rolls will likely come in 500' lengths, so it if was me...I would just use the same wire for the lamps instead of using 14awg. As fas as I know, it's ok to use 12awg on a 15A breaker. You just can't go the other way around.
Is the conduit going straight to your load center? If so...makes life easier....just terminate the wire in the load center.
However, on the load side...using stranded wire takes an extra step or so. Lights are easy...wire nut....but on the outlets, unless it is the type with a back plate on the screw, then you either have to use a pigtail with solid wire to the outlet or crimp connectors on the wire and then the connector screws to the outlet.
Personally....I prefer the crimp connectors if it's just one connection...but if your branching off to more than one outlet....then pigtail it.
Common Sense is like Deodorant. Those that need it the most don't use it.
My
and
ddawg16 is online now   Reply With Quote
The Following User Says Thank You to ddawg16 For This Useful Post:
Buzzy (09-05-2012)
Old 09-05-2012, 05:38 AM   #3
Licensed Electrician
k_buz's Avatar
You cannot use romex (NM), or the conductors inside the outer sheathing underground or outside. You will need to purchase individual THWN. The ground can be bare, but I would purchase a green #12 for the run.
Location...Location...Location
The Following User Says Thank You to k_buz For This Useful Post:
Buzzy (09-05-2012)
Old 09-05-2012, 10:06 AM   #4
Code05's Avatar
Not correct, UL lists receptacles for both solid and stranded conductors.
Twist strands CCW and they terminate just fine on screw terminals.
Code05 is offline   Reply With Quote
The Following User Says Thank You to Code05 For This Useful Post:
Buzzy (09-05-2012)
Old 09-05-2012, 02:03 PM   #5
JOATMON
ddawg16's Avatar
Yea....I know....but I've had a couple of times where one strand 'stood out' and created a problem......
Personally....the only way I would attach a stranded wire to the screw terminal without a crimp on connector is if I tinned the wire first. But that is a personal thing.
My
and
Buzzy (09-05-2012)
Old 09-05-2012, 11:05 PM   #6
Buzzy's Avatar
Thank you for your replies. I was told the following, " Ground Fault Circuit Interrupter (GFCI) protection for all outdoor receptacles is required
by the NEC – accomplished with an individual GFCI receptacle in each outlet box or with a GFCI breaker mounted in the service
panel that protects the entire circuit."
Any comments or suggestions? I plan on placing a receptacle on the front siding of my house and the other by the lamp post that will light my sidewalk. Is it okay to have two exterior grade GFCI receptacles on the same circuit?
A friend of mine told me that if I place the GFCI receptacle at the beginning of the circuit, it will provide protection coverage to the second receptacle down the line without having to install a second GFCI outlet at the lamp post.
Expense aside, I want to make sure that I am installing these receptacles properly- to code...safety is paramount.
Old 09-06-2012, 12:03 AM   #7
" Euro " electrician
frenchelectrican's Avatar
You can use one GFCI receptale for both outdoor receptales and it is pretty common to do that just remember the line and load connections just don't get them cross connected otherwise they will not work useally not kick on or stay off.
Are you putting the receptales on the lamp post ? if so which style you are going to use ? that will make the differnce on them. Also with the WP ( weather proof box ) if you going to use the GFCI's use the deep well verison due you will have more room to work around with them. ( they worth extra cost for deepwell verison )
Merci,
Marc
Old 09-06-2012, 10:45 AM   #8
Buzzy's Avatar
Merci,
Marc
Thank you for the heads up- I've installed exterior grade GFCIs in the past; one at the beginning of the circuit to cover the other receptacles down the line. I just never installed one at each location- so I wanted to make sure one did not trip the other.
At one time, I did use a GFCI circuit breaker in the load panel, but every time I would use a power tool or vacuun, the breaker would trip. So I swapped out the breaker and installed a GFCI receptacle and never had any problems.
The lamp post farthest from my house (I'm placing two into place) will have the receptacle. I'm going to build a pillar out of brick and mortar and run a stub out through the brick; and attach the the 2 x 4 weather resistant box to the brick.
As for using a deep well box, I did use one on the original install years ago for the same reasons you specified- but now Leviton makes slim profile GFCIs- and since there will be only three solid core THWN #12 wire in the box, I think there is ample room. Just the same, I had purchased a flanged box extension just in case.
I will be using the following supplies: red dot 3/4" wet location outlet box RIH32LM; if needed red dot 3/4" wet location flanged extension RIHEF6S22; red dot metal weatherproof (while in use) lockable security cover CKMU; and the Leviton 20A weather and tamper resistant slim line GFCI WT899-KW.
How far up from the ground level must the outlet box be placed?
Merci Beaucoup ~
Old 09-06-2012, 10:49 AM   #9
Lic Electrical Inspector
electures's Avatar
While your at it, you need to install a panel suitable for use as service equipment at each post and drive two ground rods at each as well.
All responses based on the 2011 NEC.
If you live in New Jersey click
. All other states click
Please check with local, county and state officials as laws may vary.
Sizing motors
. Online motor calculator
. Online calculators
electures is offline   Reply With Quote
Old 09-07-2012, 11:09 PM   #10
Buzzy's Avatar
Could you please elaborate?- I'm not sure of what you mean by this. I appreciate your help.
Old 09-08-2012, 03:42 AM   #11
E2 Electrician
stickboy1375's Avatar
I believe he was being funny, because the posts are structures.
Old 09-08-2012, 05:03 PM   #12
electures's Avatar
ANy structure supplied by more than one circuit requires a panel rated suitable for use as a service disconnect and ground rods at each structure. A post lamp is a structure. It would be easier to run a multiwire branch circuit with one constant hot and the other switched.
Sizing motors
Old 09-08-2012, 08:33 PM   #13
If you're not in a rush, depending upon your needs you can order 50' or 100' spools of thwn from the big ORANGE box store. It's cheaper than buying it by the foot but still more per foot than the 500' spool.
AandPDan is offline   Reply With Quote
Old 09-08-2012, 09:54 PM   #14
Buzzy's Avatar
Please bear with me, If I understand you correctly- for the two 7' residential light poles I'm installing on a 15 amp switched circuit (via an Intermatic ET1725C DPST timer), I have to drive 2-8' ground rods per lamp post and add a service disconnect to an existing exterior receptacle that's attached to my house siding (which is the only receptacle on a 20 amp circuit) because I want to extend that circuit out to a brick post/pillar I am building around the lamp post!?
Old 09-08-2012, 10:05 PM   #15
Buzzy's Avatar
Thank you sir for replying. Since I did buy individual lengths already, I will need to wrap one of the leads (extra length of white) in green tape to color code it as my ground since the supply house ran out of insulated ground wire. Does the green tape have to cover the wire completely by overlaying the tape to itself or can i just spiral it on leaving gaps where the white insulation will be exposed?
GFCI Panel Conduit Question passmaster16 Electrical 1 06-08-2011 11:28 PM
240v conduit with different gauge wires... Biospot Electrical 7 12-14-2010 08:07 PM
Adding ground in old home ChaosTheory Electrical 6 06-16-2010 05:02 PM
Wiring a Spa and THHN question. skleinsmith Electrical 29 04-02-2010 12:41 PM
adding new outside outlets, lights etc walt1122 Electrical 8 08-23-2007 03:11 PM