Third Sub-service Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 06-05-2007, 06:37 PM   #1
Third sub-service panel
I have a combination meter base and service entrance panel that feeds the house sub-service from a 200 amp breaker and feeds the separate garage sub-service from a 100 amp breaker.
I would like to add another 100 amp feed to another building(shop) sub-service.
Questions:
1: There is room for another 100 amp circuit breaker in the service panel. Can I supply the third sub-service from this breaker?
2: The service entrance panel has only two neutral lugs that are already being used by the two existing sub-service feeds. Can the third neutral be stacked with another in the same lug?
3: Can the feed wires for the separate services be combined in one 2 inch conduit that is used for panel to burial depth (remainder of run is direct burial) or do the services have to be in separate conduits? The wire gauge is #2 al direct burial and there are 3 wires per service (no 4th ground).
Thanks in advance,
Borderbuster
borderbuster is offline   Reply With Quote
Old 07-02-2007, 12:47 AM   #2
figured it out myself, thanks anyway,
borderbuster
Old 07-02-2007, 07:58 AM   #3
Licensed Pro
borderbuster
Hope this is what you figured out:
1. Yes
2. No
3. Would advise against using same conduit.
If the buildings are detached, you may use a three wire feed (if your AHJ approves and there are no other metallic paths between the buildings) and you will need grounding electrodes at each location. If the buildings are attached, they MUST be fed with four wires.
Old 07-02-2007, 05:45 PM   #4
Master Electrician
JohnJ0906's Avatar
A detached building may be fed with 3 wire (assuming 120/240 volts) ONLY if there are NO other metallic paths to any other building This includes metal water pipe, metal gas pipe, telephone, CATV, intercom. If there is, it MUST be 4 wire (hot, hot, neutral, grounding conductor)
Separate building also requires a grounding electrode.
John from Baltimore
One Day at a Time
"Experience is what you get when you were expecting something else"
"The bitterness of low quality lingers long after the sweetness of low cost is forgotten"
JohnJ0906 is offline   Reply With Quote
Old 07-02-2007, 08:30 PM   #5
Decided to do it the way I saw the electricians in Puerto Vallerto do it. Run one hot wire to everything, get the neutral from the ground rod.
Just kidding, except that I actually saw the electricians in mexico wiring with one hot wire only. lighting around a pool no less and wasn't low voltage either.
Had to add another neutral lug to the service entry/meter box. Added another conduit for third sub run.
There is actually room for another breaker in the meter panel but I am running out of buildings. and money.
Borderbuster
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 07:40 PM
Main Service Panel Full bobo Electrical 5 09-24-2007 07:13 PM
200 amp panel with a 100 amp service? alexz Electrical 10 07-29-2007 10:00 PM
meter to service panel mikim Electrical 5 05-04-2007 05:34 AM
Basement receptacle under service panel mekanic Electrical 2 05-12-2006 05:41 AM
