THHN Loose Wire Thru Buried Conduit? - Electrical - DIY Chatroom Home Improvement Forum
Old 03-17-2011, 12:28 PM   #1
Rewards Points: 1,062
Question
THHN loose wire thru buried conduit?
i am running 4 loose wires with 50A through 35 ft of buried conduit, from my basement to the shed. i know that XHHW is rated for direct burial but since this is not direct burial (using conduit), i was wondering if i can use THHN. it is cheaper and skinnier, i.e. should be easier to pull.
thanks
Old 03-17-2011, 12:36 PM   #2
Experienced
Jackofall1's Avatar
Yes you can use THHN conductors, but they must be in a Rigid metal conduit, or nonmetallic conduit encased in not less than 3 inches of concrete.
Mark
The Following User Says Thank You to Jackofall1 For This Useful Post:
amakarevic (03-17-2011)
Old 03-17-2011, 12:40 PM   #3
oh, i have PVC conduit but it is buried under concrete the whole way, except one 2 ft section
Old 03-17-2011, 12:51 PM   #4
Licensed electrician
Rewards Points: 1,622
Mark
Could you please provide a code article that limits the OP to just these two choices? Why does the PVC need 3" of concrete?
Also the conductor insulation would need to have a W in the rating like THWN for the wet environment. It could not be just THHN.
J. V. (03-18-2011)
Old 03-17-2011, 12:53 PM   #5
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
Mark
Huh? You can bury conduit without concrete. IMC is also rated for burial and strangely enough, so is EMT although I would never suggest it as such.
Burial depth varies based on location and type of conduit.
and NO you cannot use THHN in underground conduit. While most THHN is also dual rated as THWN, not all of it is. You must have that W in there for it to be rated for wet conditions, which underground conduit is.
edit; and Jim beat me to the punch
The Following 2 Users Say Thank You to nap For This Useful Post:
J. V. (03-18-2011), tpolk (03-18-2011)
Old 03-17-2011, 12:59 PM   #6
But just by 2 minutes. It took you longer to type the longer answer.
Old 03-17-2011, 01:22 PM   #7
Experienced
Jackofall1's Avatar
You are correct THHN without the W is not acceptable, but most THHN wire produced is also rated THWN, as for the conduit I may have been looking under the wrong section, 300.50 Underground Installations (2) Other Nonsheilded Cables.
Mark
Old 03-17-2011, 02:43 PM   #8
nap
You talking to me?
nap's Avatar
Mark
You need to look to the regulation of the specific type of conduit to determine it's acceptable uses and limitations.
Old 03-17-2011, 05:18 PM   #9
I agree with Nap on that
windows77 is offline   Reply With Quote
Old 03-17-2011, 10:57 PM   #10
Question
so before i start pulling the 4 wires through, what's the best technique? should i keep them as straight as possible to ease the pull (i have 3 90 deg turns over about 30ish ft and the conduit is 1") or is it better to intertwine them or braid them? i did pull my ADT security system wire thru today but that was a cakewalk because it was really skinny and the conduit was 0.5".
Old 03-17-2011, 11:14 PM   #11
nap
You talking to me?
nap's Avatar
NO do not braid or twist them.
For 35 feet you can possibly just push them in but I wouldn't bet on it. You need to use a pull rope and attach the wires to the rope.
especially since this is PVC conduit, use wire lubricant, and plenty of it.
and of course, it takes 2 people.
Old 03-18-2011, 08:51 AM   #12
Rewards Points: 1,594
For pulling, I used a mason's line with a bit of plastic bag tied to one end of the conduit. Had my son start shop vac at other end; air draft pulled string end with a bit of a plastic bag tied to the string (sort of acts like parachute to capture air)and done. This was about 40' with 2 elbows. I was amazed it worked.
bob22 is online now   Reply With Quote
Old 03-18-2011, 09:27 AM   #13
no interference problem with electric and security in same pipe?
The older I get the better I was
Old 03-18-2011, 09:39 AM   #14
Two conduits.
Can't fit the #6s in the 1/2" conduit.
tpolk (03-18-2011)
Old 03-18-2011, 09:47 AM   #15
Experienced
Jackofall1's Avatar
Post #10 OP has 1" buried
Tags
wire
wire in conduit silver 11 Electrical 8 04-11-2010 08:20 PM
A hot wire buried in the yard that you cannot even trip a breaker by sharting it? BJLower Electrical 3 01-21-2010 02:24 PM
Sub-Panel Wire Size and Conduit Questions Tmb9862 Electrical 3 12-02-2009 11:48 PM
What feeder wire should I use for 200amp service @ 220 feet in 3" conduit? wallstreet Electrical 5 06-17-2009 03:16 PM
loose wire lizellayank Electrical 2 03-18-2005 05:41 PM