Old 11-05-2012, 07:39 PM   #1
Is There a Maximum Distance Between Meter and Panel
1. I am upgrading a 100 amp to 200 amp service
2. The meter is a combination system that includes a service disconnect.
3. The 200 amp electrical panel (of course it also has a 200 amp disconnect) to be installed in the house will require it to be placed about 15 feet from the meter.
Questions:
1. Is there a maximum connection distance allowed between the meter and the inside electrical panel?
2. Will the connection wire between the meter and panel need to be SE 2 for copper or 4 for aluminium, or can the wire be smaller?
3. I plan to run the connection wiring in PVC conduit on side of house, any minimum conduit size?
4. Does this arrangement require me to treat the main panel in the house as a sub panel and thus remove the bonding bar?
morrisg is offline   Reply With Quote
Old 11-05-2012, 07:46 PM   #2
deverson's Avatar
230.70(A)(1) is as follows: “The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.” By closely studying the actual text in this section, it becomes obvious that the disconnect switch can be located anywhere outside the building or structure with no maximum or minimum distance from the building. However, as soon as the service conductors enter into the building, the service disconnect must be installed at the location where these unprotected conductors enter. This location will vary depending upon the construction of the building or structure and the accessibility of the disconnecting means inside the building.
The limit inside the building in Wisconsin is 8ft.
deverson is online now   Reply With Quote
The Following User Says Thank You to deverson For This Useful Post:
morrisg (11-05-2012)
Old 11-05-2012, 07:52 PM   #3
Licensed Electrician
k_buz's Avatar
Questions:
1) No max when a meter/main is installed.
2) According to my calcs, you would need 4/0 AL or 2/0 CU and a #4 AL or #6 CU for the ground.
3) You will need minimum 2" PVC
4) Yes, sub panel rules apply. No bonding jumper with grounds and neutrals separated. Water ground and ground rods need to go to the main disconnect not the sub.
Location...Location...Location
Old 11-05-2012, 07:58 PM   #4
K Buz
Thanks much for your concise answer. Very helpful.
Old 11-05-2012, 07:58 PM   #5
deverson's Avatar
I missed the service disconnect in the meter enclosure! But I think you need larger conductors from the service disconnect to the "subpanel". you don't get to used the note to 310.16in this case.
morrisg (11-06-2012)
Old 11-05-2012, 08:05 PM   #6
k_buz's Avatar
There is an exception to where you can use those sizes when you are feeding a sub panel that carries 100% of the service load. I am looking for the exact code reference.
Old 11-05-2012, 08:10 PM   #7
k_buz's Avatar
(7) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services
and Feeders. For individual dwelling units of onefamily,
two-family, and multifamily dwellings, conductors,
as listed in Table 310.15(B)(7), shall be permitted as
120/240-volt, 3-wire, single-phase service-entrance conductors,
service-lateral conductors, and feeder conductors
that serve as the main power feeder to each dwelling unit
and are installed in raceway or cable with or without an
equipment grounding conductor. For application of this section,
the main power feeder shall be the feeder between the
main disconnect and the panelboard that supplies, either by
branch circuits or by feeders, or both, all loads that are part
or associated with the dwelling unit.
The feeder conductors
to a dwelling unit shall not be required to have an allowable
ampacity rating greater than their service-entrance conductors.
The grounded conductor shall be permitted to be
smaller than the ungrounded conductors, provided the requirements
of 215.2, 220.61, and 230.42 are met
Old 11-05-2012, 08:14 PM   #8
deverson's Avatar
Well done!
Old 11-06-2012, 03:06 AM   #9
" Euro " electrician
frenchelectrican's Avatar
Questions:
Once you have main breaker at the meter socket location there is no limit on the distance however there is one item it will change the game a little which you will have to use the 4 conductor set up instead of 3 conductor which therefore it will be Black , Red , White et green or bare depending on size of conductor itself.
For full 200 amp panel normally I use 4/0 AL ou 3/0 CU however be aware some inspectors may say differnt ( commercal users are diffrent so it is not included in here ATM. )
Typically 2 " PVC useally do the trick but depending on the conductor cable. But when you start to pull 4 conductors then you will have no choice but bump up to 2.5 inch due it easier to pull it. ( I know it can get by with 2 inch on 4c's but will be pretty tough to pull )
Oui just remove the bonding screw or bar and keep the netural and ground seperated and you may end up buy the ground bussbar they useally about 10 Euros or so.
Merci,
Marc
Old 11-06-2012, 08:01 AM   #10
Great, I really appreicate the reseach that I could never dig deep enough to know what you have shared in the post.
Tags
breaker panel, conduit, distance, meter box
Section 310.15(B)(6) vs. 210.4. Don't assume, call your friendly AHJs! Daneel Electrical 3 04-11-2012 08:24 AM
Upgrading Service/Moving Panel TheAcademician Electrical 17 09-13-2011 08:48 PM
Multiple Panel Question theatretch85 Electrical 5 12-12-2009 06:26 AM
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 11:27 AM
New meter panel tomreva Electrical 3 01-08-2008 04:56 PM