Testing the ground circuit
I have just wired in a 120 v outlet. The wires were in place from a prior application and there is nothing else on this electrical line. The circuit breaker is in the off position. I discovered that the circuit neutral (white wire) and the ground wire (bare wire that gets tied to green screw) are electrically connected. I have not turned the circuit breaker on. Is this normal?
Ron Miller is offline   Reply With Quote
Old 08-22-2010, 06:12 PM   #2
Connected where....how ?
Old 08-22-2010, 06:31 PM   #3
Electrician
Proby's Avatar
Yes, this is normal for then to be connected together in the panel.
Anything fun is either illegal, immoral, or fattening.
Proby is offline   Reply With Quote
The Following User Says Thank You to Proby For This Useful Post:
Ron Miller (08-22-2010)
Old 08-22-2010, 06:40 PM   #4
Rewards Points: 869
did you test the resistance of these wires to each other, or do you see aphysical connection in the receptacle box. they are connected in you main panel, not again.
TimPa is offline   Reply With Quote
The Following User Says Thank You to TimPa For This Useful Post:
Old 08-23-2010, 04:14 PM   #5
Typically there will be 1/4 ohm between these two, depending on your wire gauge. You may be able read this low on some meters. You may need to turn all house power off to get usable readings.
Ideal makes a tester for finding "bootleg" connections between these two wires.
Circuit tester shows open neutral; multi-meter says something different. fredgmeyer Electrical 11 10-26-2009 12:41 PM
Wiring a single pole switch into a 220v circuit rlmorgan Electrical 38 10-15-2008 07:59 PM
Testing circuit with GFCI protection Hodag Electrical 4 09-15-2008 10:43 PM
Replacing wiring in middle of run, ungrounded lighting circuit alexz Electrical 3 07-05-2007 08:53 PM