Testing Circuit Breakers In Old House - Electrical - DIY Chatroom Home Improvement Forum
Old 01-13-2012, 07:35 PM   #1
testing circuit breakers in old house
to see if they trip.
Is it prudent to test thet CBs in an old house to make such they trip when overcurrent?
I have a small load center (for two CBs). I can use it to test the CBs of the old house I just bought (pushmatics bulldog).
I will put a CB rate one size higher in the small load center and then short the circuit with the CB to be tested in series. The larger CB will protect gross overcurrent while allowing the smaller CB to be tested to make sure it does trip.
Good idea?
highdeserthome is offline   Reply With Quote
Old 01-13-2012, 07:39 PM   #2
jproffer's Avatar
Rewards Points: 702
Well........
It sounds more controlled than sticking 2 ice-picks in a receptacle and crossing them.
Good idea? I dunno if I'd go that far.
What makes you think they are bad?
jproffer is offline   Reply With Quote
The Following User Says Thank You to jproffer For This Useful Post:
gregzoll (01-13-2012)
Old 01-13-2012, 07:43 PM   #3
Rewards Points: 12,794
I agree, what would make you even think of doing that?
Old 01-13-2012, 08:21 PM   #4
Rewards Points: 6,652
The only way to certify that a breaker will work as it was intended, is to have someone with the proper equipment do so, and then they have to tag it as being tested on such and such date, their initials. Otherwise, if the breakers are over a certain age (more than 30 years), suggest replacing them with new ones, along with either cleaning up the bus bar's, which have to be done while no power going to the panel, along with applying no-ox to the aluminum tails and then re-torquing the connections.
And why in the world did you split this particular question off of the original topic? Is there something else unrelated, which you would like to know, that is not related to the original question.
Old 01-13-2012, 08:32 PM   #5
jproffer's Avatar
Rewards Points: 702
I get the feeling I'm missing something. Another related thread?
Old 01-13-2012, 08:35 PM   #6
Bull Dog Pushmatic Electrical panel and Circuit Breakers
This one maybe not so much Investigating grounding for an older house
The Following User Says Thank You to gregzoll For This Useful Post:
jproffer (01-13-2012)
Old 01-13-2012, 08:59 PM   #7
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,822
We do NOT test residential breakers. We replace them. End of story.
The Following User Says Thank You to Speedy Petey For This Useful Post:
Old 01-13-2012, 10:22 PM   #8
joed's Avatar
Rewards Points: 11,518
Shorting is not a proper test anyway. You need to overload it to a specified over current and then if it trips.
Old 01-13-2012, 10:36 PM   #9
Missouri Bound's Avatar
Circuit breakers...like everything else has only so long of useful life span. If these breakers are old enough for you to question their integrity you should change them out.
The Following User Says Thank You to Missouri Bound For This Useful Post:
Old 01-13-2012, 10:54 PM   #10
Come on. You take all of the fun out of it. It is even more fun watching someone drop a Crescent wrench on a 1200 amp battery bank. Talk about watching someone piss their pants, and of course it is not me.
Old 01-13-2012, 11:02 PM   #11
Idiot Emeritus
Rewards Points: 1,492
Testing a circuit breaker at its rated voltage is a really bad idea.
Most manufacturers recommend (but do not require) that breakers be replaced if they have tripped on a short circuit. This is because after interrupting a large current at rated voltage, the contacts will become pitted and coated with copper oxide, which does not conduct well. The end result will likely be a failure at some later point, the failure could very well damage the bus that the breaker connects to.
All breakers can be tested with the proper equipment. But unless the breakers are extremely expensive or very difficult to obtain, replacement is by far the best option.
Testing a branch circuit breaker with a test set takes about 10-15 minutes each. That's pretty expensive compared to just replacing them.
The only times I've ever tested small breakers is for hospital certification, and a few industrial establishments require it.
micromind is offline   Reply With Quote
Old 01-14-2012, 12:14 AM   #12
dmxtothemax's Avatar
Rewards Points: 5,096
Testing any circuit breaker, with out a properly set up,
and safe enviroment, is just asking for trouble !
The chance of some one getting hurt is REAL !
For that reason alone most people would say
DONT DO IT !
dmxtothemax is offline   Reply With Quote
Old 01-15-2012, 08:35 PM   #13
Rewards Points: 240
I'd replace that panel. Here's the reasons why:
1. The Pushmatic is a very old design, going back to the early 1950s. The older ones are a thermal-only type of breaker, lacking a magnetic trip mechanism. This means that it works acceptably at interrupting overloads, but if a short occurs, the thermal mechanism will be slow to activate, possibly too slow to prevent an arc or fire. Also, it's conceivable that, in a short circuit, the breaker's contacts might weld before the thermal trip mechanism activates. Apparently a magnetic mechanism was added to later models, but nobody is sure when.
2. The little flags that tell you the status of the breaker are known to fail over time, so it is often hard to tell if the breaker is on or off.
3. The internal mechanisms get very stiff. This makes the breaker hard to operate.
4. Replacement breakers are expensive and don't always fit older style panels.
Also, I've seen reports that in some parts of California, electricians have found Pushmatic panel installations where there is no main breaker; everything on the line side of the branch circuit breakers is unprotected. That's obviously not a fault of the panel itself, but it is an indication of how old some of these panels are, that they were able to get away with installing it that way.
fa_f3_20 is offline   Reply With Quote
Old 01-15-2012, 08:38 PM   #14
Those were split-buss panels. Most all manufacturers had them. They are nothing out of the ordinary for that vintage.
Old 01-16-2012, 02:00 AM   #15
Rewards Points: 240
Could have been; what I said above was from a couple of Internet reports at Inspectapedia. The only Pushmatic panel I've ever seen in person was not a split bus; it had the main breaker in a separate box.
Incidentally, one cute thing about the Pushmatics was that at least some of them came with a set of stickers you could use to identify the breakers. They were pre-printed with commonly used designations like "stove", "heat", "dryer", "kitchen", "bedroom", "garage", etc. You just stuck them on the breaker handle.
Weird wiring in house fdmillion Electrical 13 06-14-2013 07:49 PM