Temporary Genrator Ground - Electrical - DIY Chatroom Home Improvement Forum
Old 05-18-2008, 10:03 PM   #1
Rewards Points: 506
Send a message via AIM to theatretch85
Temporary Generator Ground
I work for a company "On-Call" (that is they call me when the need for work arises). They have a 60kW generator that they use for large gigs (its a sound and lighting company) whether the gigs be inside or out. In any case its always temporary and never intended to be a permanent setup. My employer has bought a few 8 foot ground rods and at the end of a gig is always so determined to remove the 8 foot ground rod (which he never gets in all the way) just to save 15 bucks on a ground rod. I keep telling him to just charge the customer the 15 bucks for the ground rod and be done with it. Now my question is, I have heard that you can take 3 ground rods placed in the ground at a depth of 3-4 feet per rod and tie them together in a triangle pattern with 6 feet between any grounding rod. Making sure to bond all three ground rods together and back to the generator of course. Also, is 6AWG ground suitable for a 60kW generator on a temporary basis?
theatretch85 is offline   Reply With Quote
Old 05-19-2008, 07:22 PM   #2
Licensed Electrician
jrclen's Avatar
Rewards Points: 514
What type of loads are being supplied by the generator? If this is a portable generator, and the loads are cord and plug connected to the generator receptacle outlets, you don't need ground rods at all.
But if you are required to install a grounding electrode, I have never heard of a system of shallow driven rods as you described, being acceptable. The conductor attached to your rod or rods is not required to be larger than a #6 copper wire.
John
jrclen is offline   Reply With Quote
Old 05-19-2008, 07:33 PM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,974
Ground rods do NOT ground anything. They are pretty much useless for your application.
Old 05-19-2008, 10:05 PM   #4
Rewards Points: 506
In the event it is inspected on-site, ground rods are required. Most times its never inspected, however I witnessed on one such occasion that two generators were in use outside a school auditorium (old school that had in-adequate power for the setup) the generator we were running controlled a dimmer rack, and the other generator was setup for several tv trucks and equipment for a televised debate. The electrician wired both generators up to the same ground field, which was 3 rods in a triangle all tied together. My guess is he was with the TV station, as we didn't have him show up.
Most times the generator supplies a dimmer rack, which consists of 36 1200 watt dimmers (most often its a load of 750 watts per dimmer, sometimes more), other times it supplies a power distro for large sound applications and sometimes this includes portable dimmer packs (plug-in variety). There are 3 50amp outputs for spider boxes, plus a hardwire connection as well. This is a tow behind generator.
What I don't understand is why the one electrician at the school would have wired up three ground rods and shared them between the two generators and how that is acceptable. In this particular application, there was nothing but lighting on the one generator we supplied, so tying the grounds together to prevent ground loops would have no effect. I hope this provides enough addition information, let me know if you need anything further.
Old 05-19-2008, 11:15 PM   #5
Registered User
Termite's Avatar
When people don't understand what they're doing, they often put ground rods where they don't need them. I don't see any need for it on this application. I know of an inspector that requires a driven rod attached to the #8 copper wire used for the pool bonding grid...Completely worthless but it makes him feel warm and fuzzy because he doesn't understand what the reason for having/not having it is.
Old 05-21-2008, 12:06 PM   #6
Rewards Points: 506
Anyone else have anything to add? I mean I know that it is a requirement to have the ground rod on the generator, especially for outdoor events where power is run to multiple locations. I'd just like to know if this 3 shallow grounds is considered "acceptable". Does the NEC code book cover temporary generator codes for like outdoor events? I just bought a 2008 NEC Code book but it hasn't shown up yet, and figured talking to a few electricians on here would be easier to find the answer.
Old 05-21-2008, 02:30 PM   #7
jrclen's Avatar
Rewards Points: 514
Not meaning to insult you, but you have found the answers from a few electricians on here. You just don't wish to accept them. And that is fine.
But your 3 "shallow" ground rods are not an acceptable grounding electrode system when a grounding electrode is required. When you get your 2008 code book check out 250.53 A and G.
250.34 covers generators in regard to grounding electrodes. And 445 covers generators. You may also face state or local codes.
John
Old 05-21-2008, 11:19 PM   #8
Rewards Points: 506
Just got the 2008 Code book today, didn't quite expect it to be this big, haha. Anyway, I found the code references you mentioned regarding the grounding electrodes, and it looks like other than the shallow depth, code 250.53 C indicates that more than one rod or plate can be connected together and spaced no closer than 6 feet apart with proper wire size and connected to the electrode properly. I was just thinking about how the three shallow rods were installed and now remember that the generator we were using was at that time rented and came with the three short ground rods and were already tied together that way. So I assume the electrician for the TV crews generator must have driven the rods into the ground and just attached the ground to the same electrode system (in all honesty I can't be sure that he was an electrician). Any idea where I would be able to look locally to see if thats something allowed in my area? I would have to imagine it is somewhat acceptable if the rental place supplied the ground as 3 short rods tied together, unless the code was interpreted as 8 feet of total depth. But the code specifically says to a depth of not less than 8 feet (250.53 G).
Btw jrclen, I am just trying to figure out why it was done that way or how it is considered an "acceptable" practice to use 3 shallow grounding conductors.
Old 05-22-2008, 12:51 AM   #9
" Euro " electrician
frenchelectrican's Avatar
Really .,, 3 ground rods it just don't really do anything very well at all.
I done quite few portables units and majotry of the time it will be either one* or NONE ground rod depending on the type of load and set up.
and with what Jclen saying he is right on the target there.
Merci,Marc
{ * the ground rod size is inch size min with 3.6 meter rod [ 12 feet ]}
Old 05-22-2008, 06:50 AM   #10
Rewards Points: 506
Well actually according to the NEC code book, min size is 1/2" but should be 5/8" and it only specifies 8feet long. (250.52 5) Usually the loads are either pretty high (lighting) or fairly low (sound only). So id imagine in a low power consumption, a ground rod probably wouldn't be required where as a higher load would maybe be a good idea. We have never used a ground rod on any "portable" generator, that is to say not attached to a vehicle or a tow behind generator. Does anyone have any recommendations on when to use the ground rod and when not too? On occasion we are just using the 50 amp spider boxes usually just two at a time, others we are using the dimmer rack and direct wiring it into the generator, and still others we use a 100 amp tap tied into the generator terminals. Usually the three most common setups, on occasion there is maybe 1 or 2 of the 20 amp outlets used on the front panel, but those are GFCI outlets and on their own circuits (total of 3). Its been said on here that a ground rod isn't really doing anything with a generator, but I am sure its required if it ever gets inspected on-site (usually with larger events with multiple generators and vendors at the event).
Old 05-22-2008, 11:03 AM   #11
jrclen's Avatar
Rewards Points: 514
Take a look at 250.34. That tells you when a ground rod is not required on any portable generator. To sum it up, if the loads are cord and plug connected you don't need a grounding electrode. The size of the loads are not relevant.
If the loads are other than cord and plug, you will need the grounding electrode. This is the national code. Local code may be different and inspectors might have other ideas. That happens.
Look at 250.53. (A) requires the electrode to be embedded below the permanent moisture level. A short rod might not accomplish that. (G) requires 8 feet of length of the electrode to be in contact with the soil. If an electrode needs to be exposed above ground, a longer rod would be required so that the 8 foot rule is complied with. Close reading will make it clear the intent is for "each" electrode to comply. 16 6" rods will not pass inspection.
250.56 states a supplemental electrode may be required if the first does not have a resistance of 25 ohms or less. You can put in as many rods as you wish. But at least one would need to meet all the requirements of 250.53.
Have you ever seen one of those devises for pulling metal fence posts out of the ground? It's just a tee type outfit that uses leverage to pull the post. I bet you could come up with something similar to pull a 1/2" rod out of the ground after the concert. Just getting back to your original problem.
John
Old 05-22-2008, 05:51 PM   #12
Rewards Points: 506
Yeah I was trying to think of some possibilities to removing the rod after the event, there were 4 of us on one particular event just recently trying to pull a 5/8" rod out of the ground (that was only buried 5ft) we finally got it but it wasn't easy.
Old 05-23-2008, 09:26 AM   #13
jrclen's Avatar
Rewards Points: 514
I remembered that was your original purpose. They can be difficult to say the least. Here is the tool I was referring to.
http://www.northerntool.com/webapp/w...70_13224_13224
John
Old 05-23-2008, 06:05 PM   #14
Rewards Points: 506
Yeah the idea of that tool is good, however with it being 3 feet off the ground, it would be difficult to be able to start pulling the ground rod out of the ground (saying it goes in the required 8feet). I had thought about drilling a hole in the top of the ground rod to facilitate putting a hook of some sort on the end to have a point where something could be tied to it and use some leverage (like what you were showing in that link) to remove it. Other idea I had was to build something out of angel iron, basically a square bottom corner with a short bottom leg parallel with the ground where in the very end drill a 5/8" hole into and use that as leverage. The idea being that it would rely on the rod being pinched in the hole and would be able to move it a couple inches, drop the tool and do it again. Only this would allow for it to be a lot lower to the ground.
Old 05-24-2008, 07:03 AM   #15
What does this mean a ground rod does not ground anything?
BillyD is offline   Reply With Quote
Tags
generator , ground rod , temporary
Temporary power... MLO Electrical 8 02-18-2007 11:43 PM
Temporary support for replacement of basement beam Mikedks Remodeling 8 09-14-2006 06:36 PM