Tandem Breaker Use - Electrical - DIY Chatroom Home Improvement Forum
Old 03-18-2010, 07:13 AM   #1
Tandem breaker use
Are tandem breakers only to be used in CTL panels? I noticed that they sell non-CTL breakers. I did some research and found out they are to be used for replacements only (CTL panels have only been around for 25 years). Is a tandem breaker against code/NEC?
pomelo is offline   Reply With Quote
Old 03-18-2010, 08:10 AM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 552
If your panel allows them, they can be used.
If the panel is listed as a 20/30, them tandems will fit.
If the panel is listed as 30/30, then tandoms will not fit.
The instructions on the panel, or cover will list the model number and the type of breakers allowed.
Old 03-18-2010, 08:16 AM   #3
Master Electrician
Rewards Points: 3,920
CTL Circuit breaker-has physical size, configuration or other means which, in conjunction with the physical means provided in a class CTL assembly, is designed to prevent the installation of more circuit breaker poles than the number for whiich the assembly is designed and rated.
If the panel is designed for their use and the number of breakers does not exceed the number for which the panel is designed they are allowed.
Example: a panel may be designated a 30/40 breaker capacity. This would mean it can use 30 full size breakers or up to 20 full size breakers and 20 tandems resulting in a total of 40 poles used.
brric is online now   Reply With Quote
The Following User Says Thank You to brric For This Useful Post:
redrover (03-20-2010)
Old 03-18-2010, 08:17 AM   #4
Master Electrician
Sorry, jbfan, you beat me to it.
20 amp GFCI breaker pops when pool pump is turned on. jagrunner Electrical 11 03-19-2010 04:31 PM
tandem breaker MikeyP Electrical 11 06-29-2009 01:48 PM
Sq D Trillaint Breaker problem jmreynol Electrical 3 04-28-2009 07:06 PM
Tandem Breaker and Circuit(s) whowadat Electrical 1 01-09-2009 04:13 AM
Tandem breaker rusty_5620 Electrical 10 09-26-2007 03:03 PM