Are tamper-resistant receptacles required in unfinished basements?
I'm replacing the standard non-GFCI receptacles in our unfinished basement with GFCI's. I bought the non-tamper-resistant versions. I've installed one so far, but then wondered if they are supposed to be tamper resistant. I did some Google searching but wasn't clear if code required them in UNfinished basements. They're all less than 5 feet above the floor. I don't want to install the rest until I get this clarified. I can exchange them if necessary. Thanks.
Rav is offline   Reply With Quote
Old 01-16-2016, 07:33 AM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,968
406.12 Tamper-Resistant Receptacles for Dwelling Units
In all areas specified in 210.52, all nonlocking-type 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles.
Exception: Receptacles in the fol lowing locations shall not be required to be tamper-resistant:
1) Receptacles located more than 1.7 m (5 ft) above the floor.
2) Receptacles that are part of a luminaire or appliance.
3) A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)(7), or (A)(8).
4) Nongrounding receptacles used for replacements as permitted in 406.4(D)(2)(a).
210.52 basically covers all typical receptacles in a home, so yes, if you have a basement with power TR is required unless it is behind a large appliance.
The Following User Says Thank You to Speedy Petey For This Useful Post:
Rav (01-16-2016)
Old 01-16-2016, 07:54 AM   #3
Rewards Points: 13,960
You only need one GFI per circuit install at the begining at the line to protect all of them.
Exception, is if your working with an ungrounded circuit and your trying to convert from the old style 2 prong to having it be three pronged.
Rav (01-16-2016)
Old 01-16-2016, 08:06 AM   #4
Licensed electrician
Rewards Points: 1,750
Three prong receptacles can be installed downstream of a gfi. They do not all need to be gfi when on a two wire system.
Rav (01-16-2016)
Problems with 20A tamper-resist receptacles using 15A plugs tns1 Electrical 4 06-02-2015 05:48 AM
NEC - what is the purpose of some of these codes ? chez bouton Electrical 32 12-17-2013 02:04 PM
Is moisture resistant sheetrock required? lmorsino Drywall & Plaster 3 02-24-2013 06:16 PM
Receptacles in an unfinished basement J. Guinness Electrical 6 10-08-2012 12:30 PM
Tamper Resistant Outlets Date? ddawg16 Electrical 9 06-11-2012 05:35 PM