I have decided to install a whole house protector,but wanted to get some input from you guys first. I have no problems opening up the panel to install it,but wanted to see if anybody may see a problem that I may come across that I don't see.
Excuse the messy box,it appears it hasn't been opened in years.
http://i899.photobucket.com/albums/a...9211443751.jpg
http://i899.photobucket.com/albums/a...9211503212.jpgThe main shut off appears to be on the top right (100 amp) and it looks like I have room for a extra double pole breaker on the bottom left.
So,can I just install a double pole 20 amp breaker,attach the white wire to the buss on the right (kind of hidden) and one black wire to each of the 20 amp breaker screws and call it a day? or are there something I am over looking?
Thanks in advance.
kbsparky 03-19-2013 10:54 PM
I doubt that 100 Amp breaker is the main. The mains appear to come in to the lugs on the top. The 100 Amp may be another sub-feed to somewhere else ... is this an outside box, and directly below the meter box?
You may have a panel without a single main --- legal as long as there are 6 or fewer breakers present.
As for the surge unit, a double-pole breaker in the spare slots should do the trick.
Kev7274 03-19-2013 10:59 PM
Originally Posted by kbsparky (Post 1141167)
I doubt that 100 Amp breaker is the main. The mains appear to come in to the lugs on the top. The 100 Amp may be another sub-feed to somewhere else..... unless .... is this a mobile home? Then the lines in the top might be another sub-feed.
Best to check things out with a voltage tester.
You should have a service disconnect breaker elsewhere on the premises.
Hmm,I'll have to check and see if there is another panel,this panel is directly underneath the meter attached to the house.
It's not a mobile home.
Kev7274 03-19-2013 11:02 PM
I guess it's possible not having a main since there are only three breakers in there. Think I'll run outside and see where the main feed from the street pole goes.
Kev7274 03-19-2013 11:06 PM
Yeah,the main feed from the pole in the street feeds directly into the big metal conduit in the meter and then into the box.
kbsparky 03-19-2013 11:07 PM
You managed to catch my post between edits.
After looking at it longer, it appeared to be an outside panel, right below the meter. A wider pic showing the whole service would have been helpful here.
So I edited my post.
Apparently, I was right in the later assessment.
A "service" (panel) is allowed to have up to 6 disconnects. That makes this borderline hack job almost legal.
IF this is the service panel (first panel after the meter) then the bonding jumper should be installed. From the looks of this pic it is not. A closer look would be warranted here. IS that a neutral bar behind those breakers?
Kev7274 03-19-2013 11:13 PM
Yes the neutral bar is kind of hidden,I could get a better picture if needed.
There was an addition added to the house in years past,maybe that is what the 100 amp breaker is feeding?
Kev7274 03-19-2013 11:24 PM
http://i899.photobucket.com/albums/a...9231545904.jpg
Could the screw attached to the right of the neutral bar be the bonding jumper?
kbsparky 03-20-2013 03:36 AM
Yes on both counts. That 100 Amp breaker is for a sub-feed to another panel. And, the bonding strap is properly installed.
Use the empty slots for your surge unit. But you won't be able to turn off the power in the main panel without pulling the meter.
You'll have to call in the Power company in order to do that safely.
Kev7274 03-20-2013 09:49 PM
Am I going to have to use a Tandem 20amp in the empty spot? I only see one large tab that the breaker could snap on to.
Kev7274 03-21-2013 02:10 PM
Check picture number one.
Kev7274 03-23-2013 12:29 AM
I have been told that slot can not be used according to the wiring diagram. I guess I will have to have a sub panel installed.