I am trying to rewire an existing circuit that includes a 3-way switch controlling an outlet. I need to provide unswitched power beyond the first 3-wy switch to other lights in the same circuit. The circuit starts with 14/2 wire from the circuit breaker with 14/3 coming out of the outlet to the first 3-way switch. I have provided a link to a diagram of the layout. Is this correct? Can it be simplified?
http://www.substantis.com/gallery/al...switch_switch3
rioguia is offline   Reply With Quote
Old 10-06-2007, 12:32 PM   #2
Your diagram is electricly as simple as this will likely get. You do however have another problem. You do not have capacity in the first three way box for the device and all of the wires.
I am refering to box fill calculations. The devce counts as 2. Any clamp internal to the box counts as 1. All of the ground wires count as 1. And each other conductor that leaves the box counts as 1.
At that three way box you have 2 + 1+ 1+ 8 for a total of 12.
Table 314.16 (A) lists the deepest single gang device box as having a fill of 9 for no. 14 wire and 8 for no. 12 wire.
Master Electrician
jwhite is offline   Reply With Quote
Old 10-06-2007, 12:49 PM   #3
I understand your point. Can I avoid this problem by running single hot wire with a bare loop to each device like this.
http://www.substantis.com/gallery/album71a/power_feed
Old 10-06-2007, 01:29 PM   #4
are these all in the same box?
Since you do not count any wire that does not leave the box, pig tails, The loop idea makes no difference.
Master Electrician
Wiring double switch for new ceiling fan toolmanwannabe Electrical 17 11-15-2011 10:34 PM
Basic Switch wiring question; Dimmer to Toggle switch (Pictures included) inspectator Electrical 8 08-07-2007 02:19 AM
Ceiling Fixture / Switch Wiring gregger Electrical 1 10-21-2006 08:47 PM
When Bulb blows, Dimmer Switch Blows mAv19 Electrical 2 05-26-2006 04:52 PM
Detached garage adding a 3 way switch. Slatherd Electrical 4 01-02-2006 03:53 PM