Switched Neutral (transfer Switch) - Electrical - DIY Chatroom Home Improvement Forum
Old 11-09-2011, 06:42 AM   #1
Rewards Points: 14
switched neutral (transfer switch)
Is there an easy to understand explanation of what is happening with a switched neutral on a single phase transfer switch?
Help appreciated.
soma is offline   Reply With Quote
Old 11-09-2011, 07:40 AM   #2
Rewards Points: 1,514
The neutral as well as the hot line(s) is switched from the A side (say, utility power) to the B side (say, the generator feed).
Take a typical subpanel. The neutrals and grounds are kept separate within the subpanel but the neutral in the feed back to the main panel is bonded to ground up in the main panel. Let's suppose that the transfer switch serves the subpanel only.
With a transfer switch that does not switch the neutral (A side to the main panel, B side to the generator feed), the subpanel neutral remains bonded to ground via the main panel. With a transfer switch that does switch the neutral, when you switch to generator feed the subpanel neutral is unbonded from ground.
The switched neutral transfer switch is desirable for generators with built in GFCI protection so neutral current can't split up between the neutral and ground lines from the subject electrical system back to the generator, which would trip the GFCI's.
Old 11-09-2011, 06:33 PM   #3
Rewards Points: 14
Originally Posted by AllanJ View Post
[...]Let's suppose that the transfer switch serves the subpanel only.
I want to connect the the main breakers from the breaker box into the transfer switch without a subpanel. I guess that only leaves disconnecting the neutral from the ground in the generator?
Old 11-09-2011, 07:46 PM   #4
Switch two hots...
Switch two hots and the neutral...
Billy_Bob is offline   Reply With Quote
Old 11-09-2011, 08:03 PM   #5
You can do that too with a switched neutral transfer switch.
But here the switched neutral transfer switch won't give you any benefit over a regular transfer switch unless you have (or rerun) 4 conductors up out of the main breaker box (hot, hot, separate neutral, ground) to the meter and you separate the neutrals and grounds in the breaker box.
Why can't you connect Ground/Neutral bus bars on a sub secutanudu Electrical 42 11-07-2012 01:33 PM
Switched Neutral? sirsparksalot Electrical 10 05-02-2011 02:22 PM
Sharing Neutrals on the same phase electro Electrical 30 08-12-2010 02:10 PM
Adding a Sub Panel for Transfer Switch dcopps Electrical 27 08-24-2009 10:36 AM
Furnace Transfer Switch... caseywa HVAC 16 02-18-2008 09:14 AM