I need a bit of help. I have 110 power coming in a box, powering a 3way switch, then run to an exterior 3 way switch on an out side pole. WT, Black, Red. Green. These two switches control a light on the pole. Is there a way to also have a outlet powered at the exterior switch location that can be "always on" or does it need to be tied to the light and go on and off with the light???? Thanks for your help
bjm015 is offline   Reply With Quote
Old 10-26-2010, 09:28 PM   #2
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
there is no full time hot for the receptacle so unless you took a fulltime hot to the recep or outside switch, all you can do is have it go on and off with the light.
Old 10-26-2010, 10:35 PM   #3
Electrical Contractor
jbfan's Avatar
Rewards Points: 548
Since you only have 3 wires at the outside switch, you can't put a receptacle there at all, no neutral!
Old 10-26-2010, 10:42 PM   #4
nap
You talking to me?
nap's Avatar
well, you might be right there. I didn't pay that much attention to the count. OP said it went from the first switch to the second switch. I figured he didn't count the wires going to the light from the switch.
Old 10-26-2010, 10:48 PM   #5
jbfan's Avatar
Rewards Points: 548
I just looked at it again, and if he does not have a neutral, then he no light!
Its late and maybe I should not give advice this late.
Old 10-26-2010, 11:18 PM   #6
" Euro " electrician
frenchelectrican's Avatar
The answer is no due you only have three conductors there and two conductors are shuttle { trallever } conductors so if you want a receptale it will be switched with the luminaire otherwise you will have to run a new UF cable or Conduit to the outdoor receptale next to the post.
Merci.
Marc
Old 10-27-2010, 12:36 AM   #7
nap
You talking to me?
nap's Avatar
I'm thinking either you or I are correct. There is something missing and due to that, at best, OP would be able to install a recep that is switched along with the light and at worst, cannot install a recep at all.
Old 10-27-2010, 08:03 AM   #8
joed's Avatar
Rewards Points: 13,328
This is wrong. Since the power starts at the first switch and light is connected to the second switch, there is a neutral at the second switch. A receptacle could be installed but it would be controlled by the switch.
Old 10-27-2010, 12:49 PM   #9
nap
You talking to me?
nap's Avatar
IF the cable ran from the switch to the light and then the second switch, that white wire in the 2nd switch box could be either a traveler or the switch leg going back to the light. If whoever used XX/3 cable all the way, that is what they would end up with.
It sounds like the switch and the light may be on the same pole and if so, I suspect there is a neutral but no unswitched hot so in either situation, no full time receptacle is possible without more wire.
basic question - single pole switch in a 3-way setup dbpass Electrical 10 09-07-2010 05:29 PM
fan/light switch buzzing mjlocat Electrical 4 05-23-2010 02:44 PM
3 way switch question brons2 Electrical 11 03-08-2010 01:58 PM
Dimmer Switch Question Livewire78 Electrical 6 01-03-2010 09:51 PM
Another 3-way switch question. perpetual98 Electrical 10 07-21-2009 11:16 AM