-   -   Switch outlet in bathroom (http://www.diychatroom.com/f18/switch-outlet-bathroom-59055/)
odale 12-11-2009 02:38 PM
We have had a combination switch and outlet in our bathroom for years. Thr outlet will work only when the switch is in an off position. I have looked at the wiring and found the black hot wire connected to the brass screw on one side and the white wire connected to the other side with a small wire connecting the two screws on the white wire side. I would like the outlet to work when the switch is on or off. I have tried a new combination switch with the same results. There are only two wires in the box,a black and a white.
Michael Thomas 12-11-2009 04:10 PM
Unless this has already been done, or the bathroom outlet is already protected by a GFCI breaker, the existing switch/outlet should be replaced with GFCI switch/combo unit in any case to reduce the danger of electric shock / electrocution.
http://t2.gstatic.com/images?q=tbn:h...a11fcc_400.jpg
220/221 12-11-2009 04:20 PM
Does this switch operate the bathroom light?
If so, the recep shouldn't work at all so somethings miswired somewhere
HouseHelper 12-11-2009 04:59 PM
If that was originally a switch only (usually the case), then you only have a switch leg i.e., there is no neutral present to properly power the recptacle.
joed 12-11-2009 05:19 PM
You need at least three wire + ground for this to work properly. Replace it with a switch only device.
This was improperly installed on a switch loop. If you remove the bulbs from the light then I bet the receptacle doesn't work.
odale 12-11-2009 05:50 PM
You're right. If I take out the bulbs the outlet doesn't work. I put the bulbs back in and the outlet works when the lights are out. This has been like this for thirty years!! I just never used a plug in dryer with the lights on. Thank you all for the advice. I will replace it with a GFCI switch.
HouseHelper 12-11-2009 06:30 PM
Just putting in a GFCI switch won't work... you need another wire, either by adding an additional 12/2 or replacing what you have with a 12/3.
joed 12-11-2009 07:04 PM
You need to replace it with a switch. You can not have a receptacle there without rewiring. And since this will be a wiring change it will need to be a 20 amp circuit with #12 cable.