Switch Legs - Need Neutral, Can I....? - Electrical - Page 6 - DIY Chatroom Home Improvement Forum
Old 05-04-2013, 09:34 AM   #76
Chewy - Lic. Electrician
Originally Posted by stickboy1375 View Post
??? Want to share the light on how its a violation? READ THE VERY LAST SENTENCE OF 300.3 (B)
Yes and I did follow up with those irrelevant articles
SGC622 is offline   Reply With Quote
Old 05-04-2013, 09:34 AM   #77
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Originally Posted by SGC622 View Post
My interpretation as follows
300.3 (B) states that all conductors have to stay in the raceway for the same circuit. Unless otherwise permitted by 300.3 (B)(1) through (B)(4).
300.3 (B)(3)(which you say is your winning answer) says conductors in nonmetallic or non magnetic sheath where run in the raceways stated shall comply with 300.20 (B)
This is NOT what it says... and I already corrected you on this! You need to read what is actually written, not what you want it to say.
Old 05-04-2013, 09:39 AM   #78
E2 Electrician
[QUOTE=SGC622;1172303]My interpretation as follows
300.3 (B)(3)(which you say is your winning answer) says conductors in nonmetallic or non magnetic sheath where run in the raceways, or gutters, or cable trays or trenches or cables or cords stated shall comply with 300.20 (B)
Old 05-04-2013, 09:39 AM   #79
You are dealing with the 2011 code book right? Well you didnt prove anything I can't make you see something you dont want to see.
Old 05-04-2013, 09:41 AM   #80
E2 Electrician
I proved you are not reading the section correctly, there is a COMMA after raceways, raceways was just one example... just like CABLES...
Old 05-04-2013, 09:43 AM   #81
I did, I hope you realize I was paraphrasing and not stating it verbatim
Old 05-04-2013, 09:43 AM   #82
E2 Electrician
300.3 (B)(3)(which you say is your winning answer) says conductors in nonmetallic or non magnetic sheath where run in CABLES stated shall comply with 300.20 (B)
This is what 300.3 (B)(3) is saying.... and since 300.20 only deals with Metal enclosures or Metal raceways, it's a moot point when wiring with all plastic boxes.
Old 05-04-2013, 09:46 AM   #83
Comma or not still does not apply. You proved nothing other than our opinions differ
Old 05-04-2013, 09:48 AM   #84
E2 Electrician
I proved it was acceptable, CABLES is another wiring method other than RACEWAYS... You keep reading it as the cable is installed inside the raceway... hence the comma AFTER raceways...
Old 05-04-2013, 09:49 AM   #85
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
I was on your side, but after rereading the citation Stickboy is quoting...I agree with him. You are interpreting it incorrectly.
The Following User Says Thank You to k_buz For This Useful Post:
stickboy1375 (05-04-2013)
Old 05-04-2013, 09:52 AM   #86
I dont know if you forgot but read 300.3 (B) again. It says (and im paraphrasing) the wires are to stay in the same raceway UNLESS otherwise stated. So since 300.3 (B)(3) doesnt give an answer, it just basically tells you to reference 300.20 (B). You yourself said 300.20 (B) is a moot point. So where is your issue?
Old 05-04-2013, 09:54 AM   #87
E2 Electrician
You have yourself so convinced, you wont look at any other way...
Yes, you have to follow 300.3 (B) UNLESS otherwise permitted in 300.3(B)(1) through (B)(4)...
(B)(3) allows the installation... sorry dude.
Old 05-04-2013, 09:57 AM   #88
E2 Electrician
it just basically tells you something? lol....no, you just wont allow yourself to accept what it is saying.
Old 05-04-2013, 09:58 AM   #89
Could you please state the sentencing that wins it in (b)(3)
Old 05-04-2013, 10:01 AM   #90
I am currently in a code update class (teacher is on the code making panel). I asked it as a class question and they agree with my interpretation. So do we go separate ways and agree to disagree?
Wiring in a 4-way Switch RickSene Electrical 5 04-09-2013 07:25 PM
Transfer switch question. Adster Electrical 25 03-02-2013 08:42 PM
3 way switch layout has me confused crescere Electrical 5 09-08-2012 10:26 AM
3-way light with a twist Jeepsail Electrical 14 05-18-2010 01:24 AM
Basic Switch wiring question; Dimmer to Toggle switch (Pictures included) inspectator Electrical 8 08-07-2007 01:19 AM