Switch Legs - Need Neutral, Can I....? - Electrical - DIY Chatroom Home Improvement Forum
Old 04-28-2013, 08:52 AM   #1
Rewards Points: 344
Ok here is the problem. I need to put devices that require a neutral into a box that has 2 switches, both on the same circuit. Here is what I am thinking.
Switch A controls the porch light and Switch B controls the entry light and both have switched legs with no neutral in the box. I would like to feed both circuits from the porch light hot and use the entry neutral as my neutral.
I will try to explain in detail so hopefully I am clear.
Hot feed from porch light comes into Switch A. I would pigtail it and feed both Switch A & B. The current return leg from Switch B would be changed at the fixture and wired to the neutral (it is already a white wire). Then the old hot leg to Switch B would be the new return leg to B. Since both lights are on the same circuit, is this doable? Code compliant?
herdfan is offline   Reply With Quote
Old 04-28-2013, 09:05 AM   #2
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
No, technically that is not legal.
The circuit conductors must be grouped (hot and neutral with the exception of switch loops). Since you are bringing the hot down one cable and the neutral down the other, the circuit conductors are not grouped.
Old 04-28-2013, 09:07 AM   #3
k_buz's Avatar
300.3 Conductors
(B) Conductors of the Same Circuit. All conductors of
the same circuit and, where used, the grounded conductor
and all equipment grounding conductors and bonding conductors
shall be contained within the same raceway, auxiliary
gutter, cable tray, cablebus assembly, trench, cable, or
cord, unless otherwise permitted in accordance with
300.3(B)(1) through (B)(4).
Old 04-28-2013, 09:09 AM   #4
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
What type of wiring method?
Old 04-28-2013, 09:11 AM   #5
k_buz's Avatar
My answer was based on the assumption of NM.
Old 04-28-2013, 09:20 AM   #6
E2 Electrician
Seems that any EMF's would still cancel out with the OP's scenario...
{edit}
Eh, the cable with the ungrounded conductor would not cancel out if that load was not on....
Old 04-28-2013, 09:24 AM   #7
k_buz's Avatar
What if that "feed" was extended to power something else? True, the current on that neutral from the lighting control is almost negligible, but if that was ever used to feed a receptacle or additional lighting, there might be a much larger imbalance.
Old 04-28-2013, 09:51 AM   #8
E2 Electrician
If everything in the OP's scenario is non- metallic, I say he is good to go, although he will be creating EMF's, but thats another non NEC issue...
Old 04-28-2013, 09:53 AM   #9
k_buz's Avatar
So, how is this not a 300.3 violation?
Old 04-28-2013, 09:58 AM   #10
E2 Electrician
read 300.3(B)(3), it is an exception to 300.3.... and if all plastic boxes are used, 300.20(B) is null....
Old 04-28-2013, 09:58 AM   #11
Licensed electrician
Rewards Points: 1,256
I think he is talking about the exception if a non-metallic wiring method is used. I am not going to look it up, just off the top of my head.
stickboy1375 (04-28-2013)
Old 04-28-2013, 09:59 AM   #12
E2 Electrician
This is all ASSUMING the OP is dealing with non metallic material...
Old 04-28-2013, 10:00 AM   #13
E2 Electrician
Ever wire the travelers of a 3 or 4 way switch with just xx-2 wire instead of xx-3? same example....
Old 04-28-2013, 10:02 AM   #14
k_buz's Avatar
I don't see any exception, all I see is confirmation of my claim.
(3) Nonferrous Wiring Methods. Conductors in wiring
methods with a nonmetallic or other nonmagnetic sheath,
where run in different raceways, auxiliary gutters, cable
trays, trenches, cables, or cords, shall comply with the provisions
of 300.20(B)
. Conductors in single-conductor Type
MI cable with a nonmagnetic sheath shall comply with the
provisions of 332.31. Conductors of single-conductor Type
MC cable with a nonmagnetic sheath shall comply with the
provisions of 330.31, 330.116, and 300.20(B).
Old 04-28-2013, 10:03 AM   #15
k_buz's Avatar
No it's not the same. There is an exception in 404 for switch loops.
Wiring in a 4-way Switch RickSene Electrical 5 04-09-2013 08:25 PM
Transfer switch question. Adster Electrical 25 03-02-2013 09:42 PM
3 way switch layout has me confused crescere Electrical 5 09-08-2012 11:26 AM
3-way light with a twist Jeepsail Electrical 14 05-18-2010 02:24 AM
Basic Switch wiring question; Dimmer to Toggle switch (Pictures included) inspectator Electrical 8 08-07-2007 02:19 AM