Hello folks,
My idea is to switch a currently 120v 20amp breaker to a 240v 20amp breaker. Before I embark deeper i have a few Questions:
For what purpose are you planning on switching from 120 to 240?
You do not have a main breaker in this panel, I suspect that the main breaker (disconnect) is at the meter location. Therefore this is a sub panel. #12 wiring is good for 120 or 240 volts at 20 amps. 240 is(usually) for high power application- dryer, water heater, kitchen range, central air etc. |
A breaker marked 240 volts is allowed to be used for either 120 volt or 240 volt circuits. A breaker marked 120 volts only may not be used on a 240 volt circuit.
The same wire sizes used for 120 volt circuits (14 gauge for 15 amps, 12 gauge for 20 amps, etc.) apply to 240 volt circuits. Note that sustained (continuous) loads such as heaters or air conditioners should not more more than 80% of the breaker rating; use the next size up if needed. |
awsome thank you for the replies. i plan on installing a air conditioning unit, i wil make sure the 20a will be over 80%.
can anyone tell what guage wire i have? white means 15? |
well taking a look at my outside meter there is one box with two sections. It says on the box im only permitted to open door 2, door 1 has a lock. Inside door 2 there isn't much just a wire the comes from outside threw 2 and into 1. So without a main cutoff switch does this mean i have to call my electric company and shut off everything?? to change a breaker???
First of all, the color of the wire has nothing to do with its amperage rating. The size of the wire is listed on the cable you post in your picture, however not visible in the picture. In addition to that, you need to install a two pole breaker of the proper amperage, and proper wire size to make your installation work. You just can't add a 240v 2 pole breaker to existing wiring unlees the wiring is for a 240v circuit.
That is a main lug panel the main breaker or disconnect switch should be directely behind that panel otherwise you will have to follow the conduit where it goes { typically found below the meter socket }
Second thing if you going to use one of the exsting conductor or cable for 240 volt circuit you double check make sure there is nothing else on that circuit otherwise you will see magic smoke real quick. The safest and wisest methold is run a new circuit and be done with it. As far for breaker size for your A/C unit it will depending on what type of unit you will install that will affect the rating. Merci, Marc |
The condensing unit needs 50 amps. I install a 60 amp disconnect with 2 25 amp fuses in it. at the panel, the circut feeding the a/c is connected to a 60 amp breaker? |
On the ac unit there will be a label. This will give you the min and max amps required. You size your conductor based on the min amp listing.
Large appliances and also most air conditioners may have several amperes ratings published:
1. Running amperes 2. Startup amperes 3. Suggested or minimum amperage for the circuit feeding it 4. Maximum amperage for the circuit feeding it Running amperes for heaters and air conditioners should be no more than 80% of the wire or cable rating for example if the circuit is 30 amps then running amps should be no more than 24. Maximum amperage means that, if the appliance has 20 as max amps, you may not hook it up to a 30 amp circuit. Small plug in appliances and also lights have a max amp circuit rating of 20 amps unless otherwise noted. Occasionally startup amperes is greater than suggested circuit amperes as published. If this is the case then the manufacturer recommends a "slow blow" breaker or fuse. |
1 Attachment(s)
As far as the existing conductor goes, I'm really, really, not a fan of "magic smoke" so I'll just plan to lay down a new circuit entirly and keep the 120v 20a as itself. Thanks for the swift responses! |
bump please
Oui you got it there that is the main fuse disconnect switch.
When you hit the lever on the right side it will shut the power off to inside however some fuse box may not always the case some did have stay on at one side of the fuse while the other side is off. It good to flip the handle from time to time to make sure they are not binded up. { I know many peoples hate to reset the clocks or reboot the computer and whatever else .,, } But one major warning when you turn the main fuse lever off the top lugs will stay hot all the time so don't poke around that area either you will get electrique shock or a serious short circuit due the that lug from the meter to the upper lugs are unfused. I am glad you make a wise move to run a new circuit for that useage again verify that equiment to make sure you have proper size conductor to support that equiment. Merci, Marc |
| All times are GMT -4. The time now is 12:40 AM. |