Swimming Pool GFI Outlet For Pump/light - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 05-14-2013, 11:47 PM   #16
Rewards Points: 744
Originally Posted by mm11 View Post
"There have been 60 electrocutions and nearly
50 serious electrical shocks, involving electrical
hazards in and around swimming pools, since
1990."
Only 110 since 1990? 4.78 per year ain't bad, considering the number of above ground pools in the US. Just kidding, 1 is too many.
Seattle2k is offline   Reply With Quote
Old 05-15-2013, 12:27 AM   #17
Rewards Points: 184
I revised step 3 of my plans after researching further:
3) Run #8 solid copper wire around perimeter of pool (18"-24" from pool wall / 4-6" deep) and attach securely to at least 4 points on pool, pump motor and bond with water. Also run under walkways with 3 feet of pool in a 12" x 12" grid pattern. (Ladder and light are not metal)
stevekem is offline   Reply With Quote
Old 05-15-2013, 12:31 AM   #18
Rewards Points: 184
What I am not sure of is, can a regular gfci be used outside or is a twist lock type of outlet required?
Is a maintenance disconnect required?
Old 05-15-2013, 06:31 AM   #19
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,822
Originally Posted by stevekem View Post
Thanks mpoulton for the link to article 680 tutorial. I had a chance to read it and have come up with the following plan below.
1) Run 1/2-in PVC conduit underground direct from panel to GFI mounted at least 5ft from inside walls of pool (pool is within 10 ft of dwelling - restricted space)
A maintenance disconnect is not required correct? Pump and light both have plugs which will be plugged into GFI outlet.
You need to keep reading.
Like I said, there is SO MUCH to know it is very difficult to get it all unless you know what you are looking for.
Old 05-15-2013, 06:34 AM   #20
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
you would need WP GFI .. water proof ....
and an "IN USE COVER" ... on a waterproof box..
best i know a cord and plug would suffice as the disconnect.
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
Old 05-15-2013, 08:28 AM   #21
Licensed electrician
Rewards Points: 996
Code contradiction, the receptacle is required to be twistlock, but you will not find a pump with a twistlock cord cap.
MTN REMODEL LLC (05-15-2013)
Old 05-15-2013, 09:32 AM   #22
Rewards Points: 516
nope ....
680.7 Cord-and-Plug-Connected Equipment.
Fixed or stationary pool, outdoor spa and hot tub equipment is permitted to be cord-and-plug-connected to facilitate the removal or disconnection for maintenance or repair. The flexible cord shall:
(A) Length. Except for storable pools, the cord shall not exceed 3 ft.
(B) Equipment Grounding. The cord shall have a copper equipment grounding conductor not smaller than 12 AWG that terminates to a grounding-type attachment plug.
Old 05-15-2013, 09:34 AM   #23
Rewards Points: 516
680.21 Motors.
680.21(A)(5)
(5) Cord-and-Plug Connections. Cords not exceeding 3 ft, with an attachment plug, and containing an equipment grounding conductor, shall be permitted for pool, outdoor spa, and hot tub motors.
Old 05-15-2013, 11:54 AM   #24
JW
mm11's Avatar
Rewards Points: 592
Wow, you're hilarious. Have you ever been shocked badly? I'm guessing not.
mm11 is online now   Reply With Quote
Old 05-15-2013, 12:57 PM   #25
Rewards Points: 996
Thanks Philly, must have been a change that wasn't covered during one of the code update classes.
Philly Master (05-15-2013)
Old 05-15-2013, 02:10 PM   #26
JW
mm11's Avatar
Rewards Points: 592
WP stands for weatherproof
The Following User Says Thank You to mm11 For This Useful Post:
Old 05-15-2013, 02:20 PM   #27
Rewards Points: 516
Ok....lol I yield. Your right.... I cannot resist would that be damp or wet locations ?...
The Following User Says Thank You to Philly Master For This Useful Post:
Old 05-15-2013, 02:31 PM   #28
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
If the receptacle for the pool filter is no less than 10' away from the pool it can be a standard receptacle. However, the standard receptacle has to be horsepower rated if it is used as the disconnect. If the receptacle is not less than 6' away it has to be a twist lock, GFI protected and horsepower rated.
Of course you could always pipe it directly from the main panel with #14 black and white. Put a 25A breaker on it. Hard wire the pump and use a standard non-GFI breaker. Oh and use UF for the convenience receptacle and connect it to a general purpose circuit.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
What is wrong with my swimming pool system? Kenward Plumbing 9 05-30-2012 06:17 PM
Grounding a swimming pool bonding grid Simbilis Electrical 8 05-25-2011 12:46 PM
Wiring for swimming pool heater and salt system Scooby Electrical 1 06-08-2009 12:59 PM
swimming pool pump wire steel Electrical 5 04-06-2008 09:35 PM
Swimming Pool Water pilotandy72 General DIY Discussions 4 07-31-2007 11:04 AM