-   -   subpanels and not bonding the ground bar (http://www.diychatroom.com/f18/subpanels-not-bonding-ground-bar-171262/)
kt82 02-06-2013 10:39 PM
If you separate the neutrals from the grounds what happens if
the bare ground wire touches the back of the panel?
Or is the neutral bar that you remove the bonding screw from
to separate from the panel?
diystephen 02-06-2013 10:55 PM
The back of the panel will be tied to the ground (so entire cabinet is grounded.) The neutral bar is what is completely isolated from ground in a sub.
kt82 02-06-2013 11:19 PM
thanks makes sense .if I have #2 feeder wire my ground wire is___?
kt82 02-06-2013 11:26 PM
Are you asking how to size the;
Equipment Grounding Conductor? 250.122
Grounding Electrode Conductor? 250.66
Grounded Conductor (the neutral) 220.61
In what way is the "neutral" considered a grounded conductor?
k_buz 02-07-2013 06:01 AM
Are you answering your own questions?
Jim Port 02-07-2013 07:14 AM
I think they are looking to see if they would be using the correct article to size the conductors. They seem to have found an answer, but want someone to say whether it is correct.
kt82 02-07-2013 07:40 AM
just thinking out loud so I can frame my question
Is #6 the correct ground with #2 feeding the subpanel