Subpanel Wiring - Electrical - DIY Chatroom Home Improvement Forum
Old 03-31-2011, 11:44 AM   #1
subpanel wiring
i am wiring a 100 amp subpanel in my detached shop. running 3 #1 aluminum for 2 hots and a common, and a #8 copper for ground from main to sub panel. My question is in my main panel, the ground bus bar does not have large enough "holes" to accept the #1 common. Is it acceptable to split the #1 into 2 strands to fit into the ground bar, or is there some part that i need to screw into the ground bar to attach the #1 as one wire?
MikeyG3 is offline   Reply With Quote
Old 03-31-2011, 12:22 PM   #2
Licensed electrician
Rewards Points: 1,888
You cannot split the conductor and use two holes. Here is what one brand of adapter looks like. They should match your panel brand.
http://www.google.com/imgres?imgurl=...1t:429,r:8,s:0
Old 03-31-2011, 12:42 PM   #3
I'll look for the adaptor at the supply house. Thanks.
Old 04-01-2011, 09:56 AM   #4
grounding the subpanel
In reading through other posts, I see some things i need to do. I read that i need to separate the 2 ground bars in the subpanel--is this true? If so, does it matter which side i connect to the 2 ground rods driven into the ground outside? Also, I am bonding copper water pipe in the shop, does it matter which side i ground on?
Also, there is a green screw next to the main ground lug in the subpanel for bonding the panel. Do i need to bond the panel in addition to the 2 grounds from the main panel?
Old 04-01-2011, 09:58 AM   #5
Rewards Points: 246
You can use one of these. See picture.
Old 04-01-2011, 10:06 AM   #6
Rewards Points: 246
Yes, they must be separated and do not use the green bonding screw that came with panel. This self tapping machine screw bonds the neutral bar to the enclosure. Remove it, if it's installed.
The neutral and grounding bars are not the same thing. Usually you have to buy the ground bar to install in the panel. Just put all the grounds on the grounding bar and the neutrals on the neutral bar/bars.
Some panels have a bar that connects the two neutral bars on each side. GE comes to mind. You can remove the bar and put the neutrals on one side and the grounds on the other side.
Old 04-01-2011, 11:18 AM   #7
Master Electrician
Rewards Points: 3,964
Some panels allow you to remove the bar connecting the neutral bar and then use the bonding screw to bond the panel. This then becomes the equipment grounding bar and the other, isolated from the equipment grounding bar, is used as the neutral buss.
brric is offline   Reply With Quote
Wiring a sub panel to another sub panel Uncle Wayne Electrical 25 02-08-2011 09:50 AM
correct garage subpanel wiring lawsklsux Electrical 14 11-14-2010 10:54 PM
Yet another subpanel wiring question Chris_M Electrical 6 06-10-2010 05:12 PM
A few slightly different questions on subpanel wiring. Chris Dopp Electrical 8 06-26-2009 09:45 PM
Wiring 100A subpanel nebulous Electrical 9 08-29-2007 02:41 PM