Old 05-18-2012, 11:27 AM   #16
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
If you bought 6-3 romex, you cannot install it underground...even if it's installed in conduit.
Old 05-18-2012, 11:28 AM   #17
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
Originally Posted by Sully313 View Post
Larger conduit, done.
I'm running #6 Copper now so that gives me 65A at 75*C correct?
I am almost sure you can use UF wire at the 75 C rating but I have not ran any large UF.
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
Old 05-18-2012, 11:28 AM   #18
k_buz's Avatar
Sorry...that last post didn't show up on my phone. You should be ok...but that pull is going to be a bear.
Old 05-18-2012, 11:43 AM   #19
Rewards Points: 502
is there a 4th wire in there?
forresth is offline   Reply With Quote
Old 05-18-2012, 11:47 AM   #20
yes.. its a 10g ground. Its pulled back into the insulation a bit.
Sully313 is offline   Reply With Quote
Old 05-18-2012, 12:08 PM   #21
So, What is the correct way to run this through the wall of the house and into the garage? I'm still have doubts about my method.
Drilling big hole in the side of the house for 1.5" of conduit to go through seems a bit excessive. Would i just run the wire through the wall without conduit into the LB box? Then how would I keep the LB box in place?
Old 05-18-2012, 12:46 PM   #22
rrolleston's Avatar
I would just use conduit to get outside and into the ground and use threaded male fittings with bushings on all the ends. And be sure to use elbows on the bottom of your trench even if you decide to go direct burial.
Old 05-18-2012, 12:52 PM   #23
Licensed Pro
No need for conduit in the wall, just where it exits/enters the wall and until it goes into/out of the ground. That wire will be rated at 55A, but can be protected with a 60A breaker as long as the total load does not exceed 55A. If you can switch to 1.5" conduit, even for the short lengths, it will be easier.
Old 05-18-2012, 12:57 PM   #24
I'm having a hard time picturing where I'd use the bushings and male fittings.
Old 05-18-2012, 10:24 PM   #25
rrolleston's Avatar
Anywhere the wire exits the conduit add a threaded male fitting and a bushing to protect the wire from rubbing on the sharp edge of the conduit. Some just file the edge but I like male ends with bushings.
The Following User Says Thank You to rrolleston For This Useful Post:
Sully313 (05-19-2012)
Old 05-18-2012, 10:28 PM   #26
Missouri Bound's Avatar
Sully...where do you get those great wiring diagrams?
Do you want it your way or the right way?
Old 05-19-2012, 10:17 AM   #27
Google search for wiring diagrams led me to Stubbie's posts on this site and this site in general.
The Following User Says Thank You to Sully313 For This Useful Post:
Missouri Bound (05-19-2012)
Wire a subpanel or run separate lines? mlowrie Electrical 18 02-16-2011 06:27 PM
replacing 3 wire to 4 wire compressor fan - please advise! frazwr01 HVAC 2 06-27-2010 10:44 AM
Grounding a Subpanel Craigman Electrical 25 12-07-2009 07:25 PM
A few slightly different questions on subpanel wiring. Chris Dopp Electrical 8 06-26-2009 09:45 PM
Can i add a subpanel fed by 10/2 wire? qst4sno Electrical 25 04-25-2007 05:14 AM