Subpanel Wire Through Exterior Wall - Electrical - DIY Chatroom Home Improvement Forum
Old 05-17-2012, 05:45 PM   #1
Subpanel wire through exterior wall
First post! First I'd like to thank all of you for the wealth of knowledge here on this site. I've learned alot already!
I've been reading here for a while now and I'm finally planning on running a 220V sub panel to my garage. I think I have everything figured out but I'm not sure how to run the wire through the wall correctly. I'll be running #6 4 conductor aluminum wire to the garage with SCH40 1" PVC conduit. I'm not sure what the correct way would be to run the wire through the wall of the house and into the garage..
My current plan is to run a piece of conduit through the wall to a 1" LB conduit body like this.
Then sealed with duct seal.
Am I on the right track or am I totally off?
Sully313 is offline   Reply With Quote
Old 05-17-2012, 05:56 PM   #2
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
sounds good...what size subpanel are you planning to install?
Old 05-17-2012, 06:02 PM   #3
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
If this is where it could be hit with something you should use schedule 80 where you go up the garage and down the side of the house.
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
The Following 2 Users Say Thank You to rrolleston For This Useful Post:
Code05 (05-17-2012), Sully313 (05-18-2012)
Old 05-17-2012, 06:58 PM   #4
Code05's Avatar
Rewards Points: 1,104
Full details are required if we are to see if this install is compliant or not.
Is that a stuffy post or what?
Code05 is offline   Reply With Quote
Old 05-17-2012, 07:16 PM   #5
Rewards Points: 502
6 gauge Aluminum? that is only good for 40 amps if I am remembering correctly.
and the picture is showing it sideways, and not the proper install orientation I believe.
forresth is offline   Reply With Quote
Old 05-17-2012, 09:40 PM   #6
k_buz's Avatar
LBs can be installed whatever way you want...as long as the cover is accessible.
Old 05-18-2012, 08:49 AM   #7
I have a small 1 car garage with no options for expanding. I will only be running a Mig welder that requries a 20A breaker. The air compressor will be the next largest draw but with a 1HP motor I doubt it will pull much power.
I plan on 60A service to the subpanel.
I'm running it out of the house under the deck so that shouldn't be an issue. Into the garage should be fine too.
60A service through #6/4 AL wire through 1" conduit...... What else are you looking for? Stubbie has posted a few helpful wiring diagrams that I plan on using.
This one in particular:
Borrowed from Stubbie
This brings me to another question. A friend is trying to convince me to run a #6/2 copper wire with a 8ga ground through the PVC conduit. It's similar Stubbies diagram for a 3 wire feeder but the friend says that I don't need grounding rods. True? Which option would be better/easier?
The chart I was looking at said 55A at 70*. I thought that #6 wire would be sufficient since it will never see the full 55A.
Old 05-18-2012, 09:02 AM   #8
Licensed Pro
Your friend is wrong and three wire feeders to detached buildings are no longer allowed. To have a 60A service at the garage you will need #6 Cu or #4 Al THWN for two hots and a neutral, and a #10 CU or #8 Al THWN for the ground. Ground rods will be required.
The Following User Says Thank You to HouseHelper For This Useful Post:
Old 05-18-2012, 09:04 AM   #9
k_buz's Avatar
#6 AL isn't rated for 60A...50A max.
Old 05-18-2012, 09:11 AM   #10
ok... #4 AL it is. #6 Cu is too expensive.
Old 05-18-2012, 09:15 AM   #11
k_buz's Avatar
Do yourself a favor...forget about the 1" PVC and run at least 1 1/4" PVC.
The Following 2 Users Say Thank You to k_buz For This Useful Post:
HouseHelper (05-18-2012), Ravenworks (05-19-2012)
Old 05-18-2012, 11:09 AM   #12
Today I learned that Cu wire prices aren't that bad if you don't go to Home Depot or Lowes. I picked up some #6/3 with 10Ga ground for $2 a foot. Lowes wanted $3+
I also picked up some 1.5" conduit to run through the wall into a LB box then LB box to conduit underground. The guy at Electrical Service Supply said this wire is direct bury and no conduit is needed. T or F?
Am I on the right track now?
Old 05-18-2012, 11:11 AM   #13
rrolleston's Avatar
I second the larger conduit. You will be happy that you have the extra room when you go to pull the wire into the conduit.
Ground rods required. You have to use the 75 C rating for the wire and that brings you down to 50 amp max. And just make sure you keep your LB cover accesible.
Old 05-18-2012, 11:24 AM   #14
Larger conduit, done.
I'm running #6 Copper now so that gives me 65A at 75*C correct?
Old 05-18-2012, 11:25 AM   #15
rrolleston's Avatar
In my experience that stuff is a nightmare to pull through conduit But may not be bad for a short distance and then buried 24" below grade the whole lenth. It's a good idea to use elbows where you go into your trench and I like to use threaded ends with bushings screwed onto them. But if I can I prefer to do the whole run in conduit.
Wire a subpanel or run separate lines? mlowrie Electrical 18 02-16-2011 06:27 PM
replacing 3 wire to 4 wire compressor fan - please advise! frazwr01 HVAC 2 06-27-2010 10:44 AM
Grounding a Subpanel Craigman Electrical 25 12-07-2009 07:25 PM
A few slightly different questions on subpanel wiring. Chris Dopp Electrical 8 06-26-2009 09:45 PM
Can i add a subpanel fed by 10/2 wire? qst4sno Electrical 25 04-25-2007 05:14 AM