bmludwig 11-28-2012 12:17 PM

subpanel wire size question
 
1 Attachment(s)
I've installed a 125 amp Siemens main lug as a subpanel next to my main in the basement, I plan on powering it with a 60amp breaker from the main. I've read that 6/3 nm-b with ground can be used, so as a I was starting to hook everything up I happend to glance at the label on the panel and it says to use 2/0-4awg. Is the 6/3 too small or can I go ahead and use it? Thanks

electures 11-28-2012 01:40 PM

Smallest wire the lugs are rated for is #4. Can't use #6.

Jim Port 11-28-2012 01:49 PM

You could splice on a short length of #4 to the #6 and fit the #4 in the lugs.

joed 11-28-2012 02:01 PM

Or you could change the lugs to ones that will fit your wire.

bmludwig 11-28-2012 03:00 PM

I didn't know chaning out the lugs was allowed? I see some on the home depot site that may fit my box.

Don't really want to splice the wire.

Or I suppose I could go get some #4thhn and run it in some conduit. not at home to look at the breaker but I think #4 will fit in a 60amp

Macken 11-28-2012 07:05 PM

Just use the lugs and forget about it.

stickboy1375 11-28-2012 07:23 PM

Quote:

Originally Posted by Macken (Post 1062635)
Just use the lugs and forget about it.

We try not to endorse hacking at a DIY site... :no: