Subpanel Wire Size - Electrical - DIY Chatroom Home Improvement Forum
Old 02-14-2009, 11:12 AM   #1
Subpanel wire size
Hi,
I want to add a subpanel with four 20 amp/120 volt breakers to feed various equipment (mini-fridge, computers/laser printer, attic fan, ect). I have an unused 50 amp/240 volt breaker in the main panel which I would like to use to feed the subpanel to be located only a few feet away, so about 5-10 feet of wire. Could I use 8-3+G or should I use 6-3+G?
surrogate is offline   Reply With Quote
Old 02-14-2009, 11:48 AM   #2
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
You'll need to use the 6/3. I would just use 6/3 Al SER personally.
wirenut1110 is offline   Reply With Quote
Old 02-14-2009, 11:55 AM   #3
Rewards Points: 508
Send a message via AIM to theatretch85
I thought 6/3 AL was only suitable for 40 amps, not 50. The op would need 6/3 copper for 50 amps or 4/3 AL for 50 amps.
theatretch85 is offline   Reply With Quote
Old 02-14-2009, 12:14 PM   #4
Rewards Points: 510
It may be a 2008 thing. This cat knows very little about 08. Hoping to find something else to do when that starts around here.
I wish we could use the POCO's way of determining conductor size. Job I'm doing now I'm using 500 Cu and they're using 4/0 Al.
Old 02-14-2009, 12:23 PM   #5
Rewards Points: 510
Yeah, I just looked. It is an 08 thing. 05 didn't include 334.80 it looks like 08 does.
Old 02-14-2009, 12:50 PM   #6
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,992
Exactly.
Old 02-14-2009, 01:13 PM   #7
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
To add to that the CMP was forced thru proposal to realize that SE cables with essentially the same construction as other non-metallic sheathed cables were being used in other than 310.15 (B)(6) applications such as downstream panelboard feeders that were not mains calculated. The lack of the this controlled calculation required by inspection removed diversification considerations for after the fact sub panel feeders and similar. So it accepted the proposal to put Se in the 60 degree column as for ampacity for interior wiring. Underground USE is also 60 C ampacity depending on application. The point is it is no longer 75C but must be either 60C or table 310.15 B6 one or the other.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 02-14-2009, 01:30 PM   #8
Rewards Points: 510
I guess 310.15 (B)(6) will be next. We'll end up using 350's for a 200 amp service.
Old 02-14-2009, 02:10 PM   #9
UAW SKILLED TRADES
Stubbie's Avatar
Lets hope they don't mess with individual conductors in conduit...
Stubbie
Old 02-14-2009, 02:45 PM   #10
Idiot Emeritus
Rewards Points: 1,492
Depends on how much money the copper industry has to pony up to buy the rule change!
Rob
micromind is offline   Reply With Quote
Old 02-14-2009, 04:43 PM   #11
Thanks for the help. I bought the 6/3 NM copper. One more question, the sticker on the panel door indicates a wire size range of 2/0 - 4 for the main terminals, so is there a way to use the 6 gauge wires and the 10 gauge ground, or should I buy a different panel?
Old 02-14-2009, 07:34 PM   #12
UAW SKILLED TRADES
Stubbie's Avatar
You have Siemens panel but it must be a 125 amp panel as most 100's will take a #6. The only option I see is to use a backfed double pole breaker in the mains position. You will need the hold down kit ECMBR2 as shown below....or get a smaller rated panel to reduce the main lug size do you need one this big??
Stubbie
Old 02-14-2009, 08:01 PM   #13
No, I don't need a 125A panel, as I only plan on putting 4 or 5 20A 120V breakers in it. I think it will be easier and cheaper to return this panel and get a smaller one. Thanks for your help
Old 02-14-2009, 08:09 PM   #14
Rewards Points: 150
Stubbie:
Why do you need a hold down kit?
Steelhead is offline   Reply With Quote
Old 02-14-2009, 08:46 PM   #15
UAW SKILLED TRADES
Stubbie's Avatar
It's a requirement by the NEC for a breaker that is backfed serving as the main disconnect for the panel. The specific code is 408.36(D). They simply don't want it to be easily removed by just pulling it out by hand.
Stubbie
Size wire for Dryer Bigbobdallas Electrical 2 02-02-2009 11:47 AM
wire size for solar generator? krisman Electrical 12 01-28-2009 10:34 PM
Grounding Wire Size jamiedolan Electrical 10 01-17-2009 10:53 AM
Aluminum wire size/ guage / amps? walt1122 Electrical 17 07-30-2008 10:44 AM
Circuit breakers and wire size stan 41943 Electrical 19 03-06-2008 02:29 PM