Old 04-01-2011, 10:45 PM   #1
Subpanel Wire Questions
I am installing a 100 amp subpanel right next to my main 200 amp service panel for my basmeent re-model (both panels are GE). I've determined that I need to use 2-2-2-6 copper wire. What wire type do I need to buy? Also, if I buy four seperate pieces (as I don't think I can find a bundled wire) what do I need to do?
-Can I just run the wires from one pannel to the next through the wall? Or do they need to be protected in conduit or something?
-Can all four wires go through the same clamp at each pannel?
-I'll need to color code the wires with colored electrical tape, red and black for the two hots, white for neutral, and green for the ground? Can I color code the ground or does it have to been a green colored insulation?
-Is THHN wire appropriate?
-Anything else I'm missing?
Thanks for the help.
mykayel is offline   Reply With Quote
Old 04-01-2011, 11:15 PM   #2
Scared Electrician
Saturday Cowboy's Avatar
your wire must either be a cable or in a conduit. If you choose pipe yes THHN is acceptable. Because you must be either in a cable or conduit your wires will be in the same clamp/fitting. The ground must be green. The others are large enough that they are allowed to be phase taped. Be sure to keep the grounds and neutrals separate in a sub panel.
Ragged Trousered Philanthropist
Please follow the code - its there for your safety no matter how inconvenient.
Saturday Cowboy is offline   Reply With Quote
Old 04-02-2011, 02:35 AM   #3
Electrical Contractor
kbsparky's Avatar
You don't need anything larger than a #3 copper for your hot lines; also a #8 is sufficient for the grounding conductor.
BUT IF you decide to upsize to a #2 for the hot lines, then a #6 ground would be required.
A short conduit nipple (I'd use PVC) is sufficient as well.
-KB
Adding a subpanel to a sub-panel and other questions CardinalPilot Electrical 14 03-30-2011 03:23 PM
What type of wire for small subpanel feeder? jshattoc Electrical 6 01-23-2011 11:02 PM
Adding ground in old home ChaosTheory Electrical 6 06-16-2010 05:02 PM
Neutral Wire? 4x15mph Electrical 8 11-24-2008 02:00 PM
running wire to a detached shed subpanel amakarevic Electrical 9 03-27-2008 06:15 PM