Subpanel Vs Main Feeds Amp Ratio Limits? NEC 2005 - Electrical - DIY Chatroom Home Improvement Forum
Old 11-25-2012, 09:09 PM   #1
NJ DIY'er
Subpanel vs Main feeds amp ratio limits? NEC 2005
I live in NJ in a town that follows NEC 2005 codes. I live in a ~1800square ft. house with 1 primary electric panel. Looking for planning help to prep for design and permit application.
I'm looking to install a new sub-panel (Square D QO 100A / 20 slots / with 100A main breaker) very close to the main panel and feeding it with a 100A breaker. Does feeding 100A to the sub-panel from a main panel that is only 100A cause any code violations?
I'm looking to move a 10-12 breakers off the main to the sub and then add in a breaker to feed in a generator using an interlock kit.
I've researched other items and plan on unbonding / keeping separate neutral from ground in the sub panel. Also using #3 THHN copper with #8 ground through PVC conduit between main and new sub-panel.
Any tips and help greatly appreciated!!
Minot is offline   Reply With Quote
Old 11-25-2012, 09:17 PM   #2
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
All a sub panel does is increase the available spaces to install breakers. If you have a full 100A panel, I suspect you will need to upgrade the service to 200A, and then install the sub panel if still needed.
To start, you could list all 240V appliances...Water Heater, Dryer, Furnace, AC, Range, Hot Tub....
Old 11-25-2012, 09:43 PM   #3
NJ DIY'er
The only 240v items are:
- Dryer
- AC
If I didn't upgrade to 200A and kept it at 100A, would I be violating any codes? I am hoping I don't need to upgrade my main to 200A.
Old 11-25-2012, 09:50 PM   #4
Electrical Contractor
jbfan's Avatar
Rewards Points: 420
You do not need a main breaker in the sub, unless you already have the panel.
A 60 amp feed should be more than enough.
Old 11-25-2012, 10:12 PM   #5
" Euro " electrician
frenchelectrican's Avatar
You should be ok with the load as you posted there.
60 amp subpanel is plenty big for that useage.
Merci,
Marc
Old 11-25-2012, 10:33 PM   #6
JuzRick's Avatar
Originally Posted by k_buz View Post
all a sub panel does is increase the available spaces to install breakers. If you have a full 100a panel, i suspect you will need to upgrade the service to 200a, and then install the sub panel if still needed.
To start, you could list all 240v appliances...water heater, dryer, furnace, ac, range, hot tub....
i very well agree...
JuzRick is offline   Reply With Quote
Old 11-27-2012, 09:22 AM   #7
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
No town in New Jersey is following the 2005 NEC. AS of 11/7/12 the 2011 NEC has been adopted with ammendments. Follow the links in my signature for DIY in New Jersey.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Tags
100a , generator , interlock , square d , subpanel
Subpanel Right Below Main dcapone Electrical 6 01-02-2012 04:46 PM
Connecting subpanel to main panel rtyui2 Electrical 10 12-07-2007 06:29 PM
combining subpanel with main johnny331 Electrical 1 06-06-2007 06:27 PM
Splice box/s between subpanel and main panel? SeanR Electrical 5 05-06-2007 02:21 PM
Add subpanel or upgrade main panel dcoz Electrical 1 01-12-2006 09:24 AM