Subpanel Grounding - Electrical - DIY Chatroom Home Improvement Forum
Old 01-29-2011, 05:33 PM   #1
Subpanel Grounding
I know that if you run a subpanel then the neutral and ground must be separated in the subpanel.
My question is this: If I drive a separate ground rod for the subpanel then can the neutral and ground be bonded in the new subpanel as long as there is NO ground ran back to the main panel from the subpanel?
Thanks, Steve
Sierevello is offline   Reply With Quote
Old 01-29-2011, 05:43 PM   #2
Rewards Points: 266
Nope.
Only exception is if you are installing the sub panel in a detached building, and are on the 2005 or earlier NEC code. Not sure if you are in Canada.
junkcollector is offline   Reply With Quote
Old 01-30-2011, 02:02 AM   #3
Scared Electrician
Saturday Cowboy's Avatar
the question is not if you drive a ground rod, in most cases your are required to drive a ground rod in addition.
Ragged Trousered Philanthropist
Please follow the code - its there for your safety no matter how inconvenient.
Saturday Cowboy is offline   Reply With Quote
Old 01-30-2011, 01:08 PM   #4
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Thanks, Steve
As Junk stated if your area (jurisdiction) is under the 2005 or earlier additions and their are no local amendments to the contrary you are allowed to run a 3 wire feeder to a detached garage. You would then be allowed to bond neutral and ground in that subpanel. However you can have no other metallic paths besides the electrical feeder between that garage and the house (containing the service panel) .. where the feeder to the garage originates. This would be, as an example, a metal water line or data/phone cables, if these are in place then a 3 wire feeder is not allowed and you must run a 4 wire feeder. Any detached garage that is powered by a feeder .. meaning there is a sub-panel with circuit breaker(s) in the garage must have a grounding electrode system. So a ground rod(s) is required regardless of whether you have an equipment ground ran back to the service equipment.
If the sub-panel is in an attached garage located in the same dwelling where the service panel is located then there are no exceptions. A 4 wire feeder is your only option with neutral and ground separated in the sub-panel. A ground rod is not needed in this type of installation as the service panel has the grounding electrode system for the home.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Grounding requirement for 100A subpanel blakeasaurus Electrical 2 12-08-2010 06:59 PM
Grounding a Subpanel Craigman Electrical 25 12-07-2009 08:25 PM
Adding second grounding bar to subpanel rdy2go Electrical 11 09-13-2009 08:59 PM
Subpanel grounding CAUTIOUSHOMEOWNER Electrical 30 12-02-2008 05:08 PM
Grounding electrode at subpanel Randell Tarin Electrical 18 02-01-2008 10:05 PM