I went into my basement today to shut off a breaker on my subpanel and noticed something that I wanted to check on. The current main panel has 3 wires running into it (2 hots and a ground). The main has a shared neutral and ground bar (which I believe is ok, based on the little I know about electrical). My question, though, is about the subpanel. It is currently fed by a 50 amp breaker connected to the main. Coming into the subpanel are 3 wiresÖ two hots that connect to the main portion of the panel and a neutral that connects to the neutral bar. There is no ground bar in the subpanel, and all of the ground and neutral wires coming into the subpanel connect to the neutral bar. Iím not sure how long ago the subpanel was put in, but I believe it may have been put in by a homeowner, hence some of my concern. Anyway, my questions are:
  • Does this mean my subpanel isnít grounded?
  • Is this dangerous?
  • Should I fix this, and if so how?
Thanks so much!
buchman is offline   Reply With Quote
Old 06-23-2012, 12:17 PM   #2
Master Electrician
the rules on subpanels changed awhile back. nowadays you can't have the neutral and grounds bonded in a subpanel. if the subpanel is in another building i believe you also have to have a seprate ground rod system, plate etc. in place as well.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 06-23-2012, 12:29 PM   #3
Electrical Contractor
kbsparky's Avatar
No. It is grounded through the neutral.
Is this dangerous?
Possibly so. Keep in mind that your neutral is a current carrying conductor, while the ground wires are not.
It IS a violation of the Code ....
Yes, fix it.
You will have to use a 4-wire feeder to the sub-panel. If it's fed with individual wires in a conduit nipple, then simply add another conductor. If it's fed with a cable assembly, then you will have to replace it with a conduit/nipple or a proper 4-wire cable.
Then install an equipment grounding bar kit in the sub-panel, and relocate all the grounding conductors from the neutral to the new ground bar. Remove any bonding jumper or screw in the panel to isolate the neutral from the grounds.
-KB
Old 06-23-2012, 12:36 PM   #4
Awesome... Thanks so much for your help!
buchmana is offline   Reply With Quote
Old 06-24-2012, 11:04 AM   #5
Rewards Points: 246
Actually this was only made illegal on the 2008 code cycle. It was perfectly legal before then. You do not have to do anything. But have at it if you want to.
Old 06-24-2012, 12:07 PM   #6
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
As long as I've been an electrician (14 years) the grounds and neutral have needed to be separate. Is there metal conduit between the main and sun panels? If so, you will not need to mess with running a new ground between panels.
Old 06-24-2012, 12:18 PM   #7
Semi-Pro Electro-Geek
Rewards Points: 2,990
I thought that was changed in like 1996. Definitely older than 2008.
mpoulton is offline   Reply With Quote
Old 06-24-2012, 12:44 PM   #8
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
No way, where did you read that? You must be referring to "detached" structures.
Subpanel Grounding Sierevello Electrical 3 01-30-2011 12:08 PM
Grounding requirement for 100A subpanel blakeasaurus Electrical 2 12-08-2010 05:59 PM
Grounding a Subpanel Craigman Electrical 25 12-07-2009 07:25 PM
Grounding electrode at subpanel Randell Tarin Electrical 18 02-01-2008 09:05 PM
Anyone want to take a shot at why #6 to attach antenna ground to breaker? Piedmont Electrical 44 01-08-2008 04:11 PM