Old 09-17-2008, 03:59 PM   #1
subpanel feed neutral conductor connection in main panel
what do you do if the neutral conductor on a subpanel feeder cable (awg3) is too large to fit in one of the free openings in the main panel's neutral bus - can you split the strands and run half into 1 of the screw connectors in the bus, and half into the another, or do you need to add a (larger) lug connector - if so, would this lug just clamp onto the existing bus?
thanks
-randy
rtoni is offline   Reply With Quote
Old 09-17-2008, 04:28 PM   #2
electrical contractor
do NOT split the strands, put in a neutral lug kit.
Jimmy
Life is tough, Life is tougher when you are stupid.
wire_twister is offline   Reply With Quote
Old 09-17-2008, 04:55 PM   #3
thanks Jimmy - will do....
Old 09-17-2008, 05:08 PM   #4
Moderator
Termite's Avatar
A solderless lug is a must!
Old 09-17-2008, 05:29 PM   #5
thanks kctermite - it's now on my things-to-pick-up list on the way home tonite
feeling a little less clueless now...