-   -   subpanel feed neutral conductor connection in main panel (http://www.diychatroom.com/f18/subpanel-feed-neutral-conductor-connection-main-panel-26964/)
rtoni 09-17-2008 03:59 PM
what do you do if the neutral conductor on a subpanel feeder cable (awg3) is too large to fit in one of the free openings in the main panel's neutral bus - can you split the strands and run half into 1 of the screw connectors in the bus, and half into the another, or do you need to add a (larger) lug connector - if so, would this lug just clamp onto the existing bus?
thanks
-randy
wire_twister 09-17-2008 04:28 PM
do NOT split the strands, put in a neutral lug kit.
rtoni 09-17-2008 04:55 PM
thanks Jimmy - will do....
Termite 09-17-2008 05:08 PM
A solderless lug is a must! :thumbsup:
rtoni 09-17-2008 05:29 PM
thanks kctermite - it's now on my things-to-pick-up list on the way home tonite
feeling a little less clueless now... :blink: