-   -   Subpanel in detached garage (http://www.diychatroom.com/f18/subpanel-detached-garage-29537/)
gp_wa 10-07-2008 02:55 PM
Another subpanel thread, yay! Searched, didn't find.
Subpanel in a detached garage, fed from 100 amp breaker in main panel. Do I have to maintain ground/neutral separation back to the main panel, or do the ground rods take care of this?
jerryh3 10-07-2008 03:05 PM
Yes. Seperate the ground and neutral. You'll still need a ground rod at the garage.
gp_wa 10-07-2008 03:24 PM
Thanks.
Somebody said grounding (subpanels) is a complicated issue. Is there any condition where one doesn't have to maintain ground/neutral separation?
jerryh3 10-07-2008 04:06 PM
Originally Posted by gp_wa (Post 169372)
Thanks.
Yes, it's complicated. Yes, there are conditions where they aren't seperated, but not in your situation.
InPhase277 10-07-2008 09:27 PM
Well, that actually depends on if there are any other metallic paths between his detached garage and the house (water lines, phone/cable, etc) and what code is in effect in his area. The 2005 code and earlier allows for a three-wire feed, with the neutral and EGCs bonded in the panel, and to a GEC. 2008 code has discontinued that practice. But, for safety's sake, I never like to use the three wire solution. So yes, use four wires.
Marvin Gardens 10-07-2008 10:02 PM
I like the 4 wires also and do that on all my remote buildings.
Stubbie 10-07-2008 10:11 PM
Washington State has a statewide electrical code and it is mandatory that 4 wire feeds be installed to all panels load side of the service equipment to residential detached structures/buildings. Best I can tell this has been in effect as a state amendment to the NEC since 1999.