Subpanel Circuit Hot With Breaker Tripped - Electrical - DIY Chatroom Home Improvement Forum
Old 08-24-2011, 03:14 PM   #1
Question
I installed a sub panel in my barn, about 175 ft from my main panel, which is 400 amp, used a 60 amp breaker in the main panel. I ran 3-#6 plus ground, to the sub, no main breaker in the sub. Everything seemed to work properly, (my tester light lit up when I put the probes on the hot side of a 20 amp breaker in the sub, and on the neutral). The problem came when I started to run my first circuit, which was a 20amp receptacle. When I test it, it appears to work. However, when I trip the 20 amp breaker, there is still current flowing, although the light is very dim. Could this be a grounding issue? I intend to use grounding rods at the sub, but haven't installed them yet.
Thanks for the help!
diyjunkie is offline   Reply With Quote
Old 08-24-2011, 03:47 PM   #2
Missouri Bound's Avatar
What light? What type of tester? 60 amp 2 pole breaker I'll assume. It's unlikely you have anything but phantom voltage there. You need an a analog tester, perhaps something like a Wiggy. Take the breaker out in the main and then check at the sub for voltage...I wouldn't be surprised if your light still glowed dimly.
The Following User Says Thank You to Missouri Bound For This Useful Post:
diyjunkie (08-24-2011)
Old 08-24-2011, 03:58 PM   #3
Thanks Missouri
Yes, the 60 amp breaker is a double pole. The tester is just a little light with two probes on it--I got it at HD for a few bucks. I do want to invest in a better tester, since I plan to do more of this. I did try temporarily disconnecting the 20 amp circuit ground wire at the subpanel, and the light went out, which led me to believe it might be a grounding issue. I'll try what you suggested when I get home tonight. If I do have a "phantom" voltage, is that something to worry about?
Thanks.
Old 08-24-2011, 05:40 PM   #4
dmxtothemax's Avatar
Rewards Points: 5,496
Phantom voltages are usually nothing to worry about,
You can easily make your own voltage tester,
Just use a standard incandesant lamp,
& a lamp base with a cord on it.
Simple, cheap, effective.
I would bet that with a tester like that
no significant voltage would be present.
Or use a good old anologue style volt meter.
dmxtothemax is offline   Reply With Quote
The Following User Says Thank You to dmxtothemax For This Useful Post:
Old 08-24-2011, 07:03 PM   #5
Code05's Avatar
Rewards Points: 1,104
How did you pass inspection with no ground rods? What wiring methods are you using in this barn?
Code05 is offline   Reply With Quote
Old 08-25-2011, 08:39 AM   #6
I=E/R
a7ecorsair's Avatar
This ungrounded sub panel, does it have a separate ground bar that is isolated from the neutral bar?
a7ecorsair is offline   Reply With Quote
Old 08-25-2011, 08:51 AM   #7
I added a ground bus to the panel. The neutral bus is isolated from the ground bus and from the panel itself. I plan to run 2-20 amp circuits--one for lights and some fans, and one for receptacles. Also one 220 volt receptacle to run a welder and power tools. None of that is done yet--I ran into this issue with my first run to a receptacle just to see if things were working.
Old 08-25-2011, 08:55 AM   #8
Code05's Avatar
Is this a real barn with livestock/animals or a shed/workshop?
Old 08-25-2011, 09:12 AM   #9
i would install ground rod and run to the panel.also check the amps on any equipment you intend to be using.
mickie is offline   Reply With Quote
Old 08-25-2011, 09:45 AM   #10
It's a small, "real" barn. Four horse stalls and two tack rooms, plus an area under cover to store hay and grain. I have a separate work shop near the house, but I want to be able to bring power tools out to the barn when I have a project there, particularly the welder.
To Mickie: I'm planning to put in at least two ground rods before I start using the system, but haven't gotton to it yet--we've been having record high temps both during the day and at night--too hot for humans.
Old 08-25-2011, 09:56 AM   #11
Code05's Avatar
You got a code book? You have to wire it according to Article 547.
Old 08-25-2011, 10:43 AM   #12
Thanks to all--the discussion was very worthwhile to me. I'll attack it again as soon as it cools off a bit.
Wanting to add a circuit breaker subpanel to fuse panel. humberguy Electrical 6 06-24-2011 10:18 PM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM
small voltage on circuit with breaker off jasonmechler Electrical 3 08-24-2009 08:52 AM
Circuit out but circuit breaker didn't trip PaulenAndrew Electrical 17 08-16-2008 08:38 AM
Circuit breaker panel - Advice needed justtired Electrical 15 12-13-2007 05:55 AM