Old 09-16-2012, 08:50 PM   #1
Sub panel wiring
Can I use 2-2-2-4 mobile home feeder to wire a 100amp subpanel in my new garage 300 ft from my house
hardgear69 is offline   Reply With Quote
Old 09-16-2012, 09:00 PM   #2
deverson's Avatar
Sub panel wiring
Depending on the load you plan on using you might have to upsize the wire to account for voltage drop.
You should be alright up to 60 amps with copper wire.
deverson is offline   Reply With Quote
Old 09-16-2012, 09:01 PM   #3
deverson's Avatar
Sub panel wiring
You should be alright up to 609 amps with copper wire.
Don't forget the 2 ground rods at the subpanel
Old 09-16-2012, 09:28 PM   #4
Sub panel wiring
Did I miss something .... 609Amps?
Gac66610 is offline   Reply With Quote
Old 09-16-2012, 09:32 PM   #5
Missouri Bound's Avatar
Sub panel wiring
ding ding ding.....we have a winner.....NOT!
Do you want it your way or the right way?
Old 09-16-2012, 09:38 PM   #6
Sub panel wiring
Two ground rods?
Old 09-16-2012, 09:41 PM   #7
Sub panel wiring
You probably will not use the full 100 amps.
Do you know what the loads will be in the garage?
IF you want the full 100 amps you would need to run 4/0 AL or 2/0 CU.
IF you know the loads the wire can be sized for it.
EDIT: that will meet the voltage drop 'recommended' by the NEC.
There is nothing saying that this is required, check local building codes
Old 09-16-2012, 10:24 PM   #8
Electrical Contractor
kbsparky's Avatar
Sub panel wiring
The short answer is NO!
#2 mobile home feeder is not rated for 100 Amps under the circumstances you have outlined. #2 Aluminum wire is only good for 90 Amps in this scenario. It's only approved for a 100 Amp service as the sole feed for a dwelling unit. Since a detached garage does not qualify as a dwelling unit, you are limited to 90 Amps.
You can still use a 100 Amp panel in the garage, but connect the #2 feeder cable to a 90 Amp breaker in your main house to be compliant ..... UNLESS ...
If you want to deal with voltage drop issues, then you will have to increase the wire size relative to your connected load. Once you increased the wire size, then you will be able to use a 100 Amp breaker at the house.
While there are many posts here that calculate voltage drop based on a full 100 Amp load, in real life that is rarely the case.
Have you performed a load calculation on the garage?
-KB
Old 09-16-2012, 11:07 PM   #9
deverson's Avatar
Sub panel wiring
ipad keyboard and fat fingers.!
Old 09-16-2012, 11:09 PM   #10
Sub panel wiring
Well...thanks for explaining that. Everyone here is judged by their posts...me and you and everyone else.
The Following User Says Thank You to Missouri Bound For This Useful Post:
deverson (09-16-2012)
help wiring a panel ex-28 Electrical 17 01-27-2012 03:51 PM
Sub Panel GND and mixed 240/120 VAC branch curiousB Electrical 12 01-17-2012 11:49 AM
wiring sub panel right next to main panel bill423 Electrical 4 05-14-2011 09:17 PM
Wiring a sub panel to another sub panel Uncle Wayne Electrical 25 02-08-2011 10:50 AM
Sub panel wiring question mntnvew Electrical 13 03-02-2009 12:28 PM