Sub Panel And Wire Guage - Electrical - DIY Chatroom Home Improvement Forum
Old 08-17-2008, 04:09 PM   #1
Sub Panel and Wire Guage
Hello,
I will likely be installing a sub panel that will provide 100-120 amp service to a section of my house. What is the appropriate wire guage to supply the sub panel, and what would I need to run the wire in (conduit, flex?)?
Thanks.
budhead is offline   Reply With Quote
Old 08-17-2008, 06:42 PM   #2
Electrician
Originally Posted by SD515 View Post
Unless the conductors are part of a listed cable assembly, yes you would use an approved conduit wiring method, which is the way I would do it. Tbl 310.15(B)(6) allows residential services and feeders (certain conductor types:double check, but you'll most likely be using one of those types) to use sizes:
You cant use table 310.15(B)(6) for a subpanel.
chris75 is offline   Reply With Quote
Old 08-17-2008, 06:58 PM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
We do.
At least for 100A. We use #2AL or #4CU.
Old 08-17-2008, 06:59 PM   #4
Electrician
SD515's Avatar
Rewards Points: 504
I thank you chris, and I apologize. I re-read 310.15(6) and agree with you, and see my mistake. I retract my post.
Old 08-17-2008, 07:02 PM   #5
Electrician
Originally Posted by Speedy Petey View Post
We do.
A lot of people do.... i'm just posting the correct information. I just install a 90 amp breaker.
Old 08-17-2008, 07:13 PM   #6
I know, and I agree. I was more playing than anything.
Again, it comes down to giving the broad correct advice as opposed to what they let you get away with at home.
Old 08-17-2008, 07:20 PM   #7
electrician
We do.
Well I've had my couple more and now I'm fine. We are also allowed to use T310.15(B)(6) for residential garages, Damn I am lucky to have my inspectors
Silk is offline   Reply With Quote
Old 08-17-2008, 07:26 PM   #8
Electrician
If the garage is detached then its not even a dwelling unit.... how messed up is that, so you actually have a state amendment for that?
Old 08-17-2008, 07:43 PM   #9
electrician
No state amendment, just been accepted practice for umpteen years. One of the new inspectors around 3 years ago tried to enforce it, and all the contractors went over his head to the regional inspector and he got spanked and eventually quit. I guess our inspectors are more reasonable because we don't rely on building inspectors. We use electrical inspectors who are all licensed electricians so they understand the concepts behind the NEC and are not just enforcing the rules to the letter.
If you understand that T310.5(B)(6) is derated because the total load will more than likely never be used, then the same concept holds true for a residential detached garage were most people will only be using a couple of 8 foot flourescent lights and maybe be recharging their weedwacker on a 100 amp panel.
If the homeowner is known to be a welder or mechanic or some other type of tradesman then we all know that the inspector would prefer that we don't use the table because he will probably be moonlighting out of his garage/shop.
So you see, if everybody in the loop is competent, then a little leeway is not over the top. As professional tradesmen we should be allowed to use some of our own best judgements, otherwise any old monkey could just "follow the rules".
I could tell you a few more doozies, but it's Sunday an I wouldn't want anybody to get jealous because I think it's against "the rules" to "covet thy neighbors inspector"
Old 08-18-2008, 10:10 AM   #10
Mechanical Engineer
comp1911's Avatar
Rewards Points: 150
We do.
Same here in MN.
comp1911 is offline   Reply With Quote
Old 08-18-2008, 04:02 PM   #11
Electrician
Originally Posted by comp1911 View Post
Same here in MN.
If you guys are using SER type cable, the 2008 nec will require it to be rated at 60 degree table, so it will only be good for 75 amps, instead of the current 90 amps that everyone still uses 100 amp breakers for, even though its a code violation.
Old 08-18-2008, 04:24 PM   #12
I do agree with you there Chris. 2008 does clarify this.
Without getting into the same old debate, I do strongly disagree with you, that using a 100A right now under our circumstances, is a code violation.
It is merely a difference in interpretation by our AHJs.
Old 08-18-2008, 04:34 PM   #13
Electrician
No big deal, my local inspectors dont know squat, I could use a 125 amp breaker if I wanted too...
Old 08-19-2008, 02:53 PM   #14
Mechanical Engineer
comp1911's Avatar
Rewards Points: 150
Old 08-19-2008, 04:18 PM   #15
Electrician
I know my post was supposed to be funny, but in actuality, its the sad truth, we have building inspectors (usually some wanna be fire department volunteer, that inspects every trade.
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 07:40 PM
Melted Service Entrance Wire in Panel theatretch85 Electrical 13 08-22-2008 10:37 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM
Pool Sub Panel wire / conduit questions Al the Diy guy Electrical 23 02-03-2008 02:32 PM
Splice in Neutral to Panel - OK or Not? allpraisebob Electrical 4 08-12-2006 05:54 AM