If I add up all the circuits, it is 95A. The way it's set up there is no chance more than 60A will be running at one time. Would a 70A breaker in my main panel work or should I go higher?
I think they add up to 85 amps? 30+20+20+15 = 85 amps Anyway you don't add the breakers its the load they serve that matters. But adding the breakers would certainly make your feeder breaker big enough.....
Since your serving a pool this will be a pool feeder and will need to be ran in conduit all the way from panel to panel. Use pvc. All conductors must be insulated and the ground (green) also.You didn't say if indoors or outdoors for the pool location. The sub-panel needs to be 3r rated for wet conditions if you mount it outside. A 6 space 12 circuit panel will be a good choice this will allow you one extra space than what you are listing as the required # of circuits. The 12 means that if you install all 120 volt single pole breakers that are the tandem style you can get 12 circuits.
However all your breakers that you will be installing to serve the pool are gfci and will be full size breakers so you will use up all but one of the six spaces. You could use the last space for other uses. If you put in a 20 amp tandem breaker in this space you could generate two 20 amp branch circuits. Regardless whatever panel you buy needs 5 full size spaces most will be 6 or greater in the 100 amp class.
Without the actual load requirements of the pool... sizing the feeder is not possible at least if you want it sized to the minimum requirements of the pool equipment. Without those numbers I would go with the main panels maximum bus stab rating. If your main is 100 amps it is probably going to be somewhere around 70 or 80 amps max. branch circuit or feeder breaker. This should be on the panels cover specifications sheet. If not post the panel model # and I'll check for you. With that we can size the maximum feeder the panel will support.
This appears to be a decent load that will have to be supplied from the main panel so if it has a lot of demand on it presently, before the addition of the endless pool, you have a possibility of the main breaker tripping out on overload.
Bone up on pools/spas art. 680 you can read it here........ starts on page 16
http://www.mikeholt.com/files/PDF/Pooldownload.pdf
Stubbie