Sub panel questions
So because I cannot have a common neutral/ground in the sub-panel how do I deal with running all the grounds to one side and neutrals to the other? The 40 space Siemens box has two isolated bars, that may/may-not be common.
Can I/ should I connect them and add a ground bar kit? But then I don't have a big lug connection for the ground.
Should I split them and run all the neutrals to one side and grounds to the other?
bkvanbek is offline   Reply With Quote
Old 08-26-2011, 09:38 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 224
Most siemens panels have a copper jumper from one bar to the other.
Disconnect the bar, install the green screw on one of the bars, and use that as your ground, and the other bar as your neutral.
Old 08-27-2011, 09:22 AM   #3
Rewards Points: 77
It just seems kind of messy to run all the grounds to one side and all the neutrals to the other.
Old 08-27-2011, 09:43 AM   #4
I know it's tedious... but ground and neutral must be isolated, unless you go through a transformer in which case you may connect the two.
asfyxation is offline   Reply With Quote
Old 08-27-2011, 10:05 AM   #5
Rewards Points: 77
Is it not worth it to have two neutral bars and two ground bars, one of each on each side?
Old 08-27-2011, 11:07 AM   #6
That's new to me, so I can't answer on that. However if your panel is rated for it, you can double up on the wires to save on space. Definitely check to make sure though.
Old 08-27-2011, 11:23 AM   #7
jbfan's Avatar
Rewards Points: 224
Nothing stopping you from doing that, but time and money!
Old 08-27-2011, 02:48 PM   #8
Code05's Avatar
Rewards Points: 1,104
Nope.
408.41 Grounded Conductor Terminations. Each
grounded conductor shall terminate within the panelboard
in an individual terminal that is not also used for another
conductor.
Code05 is offline   Reply With Quote
The Following User Says Thank You to Code05 For This Useful Post:
asfyxation (08-28-2011)
Old 08-29-2011, 05:00 PM   #9
Sounds like the same box I have in my garage. All of the grounds are connected to the left bar. The copper ground cable is connected at the bottom hole. There is a tab bonding the ground bar to the box.
All of the neutral wires are connected to the right bar. The bracket that connected the two bars was removed (and is laying at the bottom of the box).
They did a very neat job running the wires. The ground and white separate where the Romex comes in the box. The wires are routed along the edge of their respective side and then make a 90 degree bend and run to the hole in the bar, starting with the top hole.
brgmgb is offline   Reply With Quote
More Sub Panel Questions rdkng07 Electrical 6 05-25-2011 09:46 AM