Old 08-15-2011, 12:33 PM   #16
Yes I plan on putting in a sub panel either way. I'm just asking if I need to install a main breaker panel since I want more than 6 slots. Or can I use a main lug. Gas appliances.........but well pumpp, pressure tank, central air, dishwasher, mechanical septic.....I don't believe I would be coming close to overloading my panel
dimyself121 is offline   Reply With Quote
Old 08-15-2011, 12:48 PM   #17
Sorry...I don't believe I will be overloading my service.....what are the possible consequences of not pulling a permit
Old 08-15-2011, 12:55 PM   #18
Rewards Points: 6,652
Not pulling a permit, when you get ready to sell the house, they could come back and tell you to open everything up, and charge you a killing, and worst case, have you rip everything out. As for load, it depends on what you plan on running at the same time out there, that could stress the system for the rest of the house, is really the only thing I can think of with adding more onto your existing service.
Post the brand & model of the current panel, and if you have questions about hooking up, can post pictures of the panel with the cover off of it.
Old 08-15-2011, 02:40 PM   #19
Learning by Doing
Leah Frances's Avatar
If you don't pull your permits and your HOer's insurance finds out about it they will drop you. If you get dropped you're gonna have a bad problem with your mortgage.
Also, if you have a fire and they find out they will not pay.
If I could only remember to THINK about what I was doing before I did it.
Leah Frances is offline   Reply With Quote
Old 08-15-2011, 09:42 PM   #20
Panel Type
If I want a sub panel with more than 6 spots in my attached garage, should I use a main breaker panel or a main lug panel? And can I use either or? I have read if you have more than 6 breakers in your sub. It cannot be main lug. Is this true?
Old 08-15-2011, 10:50 PM   #21
A main panel can be used as a sub. You just have to size the upstream breaker in the main panel accordingly. It depends on your load, and since you plan on doing 60 amp, no more, you could keep the 100 amp in the panel you want to use, just use the 60 amp breaker in your main, and wire per spec's as already noted. As long as you do not exceed six throws for disconnect, you should be fine.
Sit down and draw out what you want on paper, then find out what you need to file for the permit. You can purchase all of the materials and have them ready, just until you get the permit, you are unable to perform any scope of the work, with the exception of doing planning. You should be able to get it done in one weekend, as long as no one bothers you to have to go do errands, etc.
Old 08-16-2011, 10:24 AM   #22
So it's true that you can't have more than six breakers in a subpanel
Old 08-16-2011, 10:29 AM   #23
Code05's Avatar
Rewards Points: 1,104
Nope.
Code05 is offline   Reply With Quote
Old 08-16-2011, 10:29 AM   #24
Master Electrician
Rewards Points: 3,698
No, it is NOT true.
brric is online now   Reply With Quote
Old 08-16-2011, 10:32 AM   #25
So gregzoll's last comment is incorrect ...please explain
Or does he mean? IF I exceed six pulls I need a main breaker panel
Old 08-16-2011, 10:51 AM   #26
Code05's Avatar
A sub panel in the same structure does not need a main nor is it limited to 6 breakers.
Old 08-16-2011, 11:34 AM   #27
Six throws to disconnect, means that it should not take more than six moves to disconnect power from any device on any panel. You can have as many breakers as the panel can handle. In commercial applications, you have a main, then a panel for subs or large tools, then a lighting panel, panel for receptacles, and also if the application warrants, a panel for a genset.
In your application, since you are just installing that sub to allow for growth out in the garage, if you only need six breakers to supply all of the tools you are going to be using, due to most likely will not be hard wiring any, and may have two that use the same receptacle, you may only need six.
Keep in mind, that you are going to have to sit down and draw up what you exactly what to do with this space, regarding having convenience outlets and convenience lighting possibly on that panel, along with the breakers for the larger tools.
The Following User Says Thank You to gregzoll For This Useful Post:
dimyself121 (08-16-2011)
Old 08-16-2011, 11:39 AM   #28
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
The six motions of the hand rule applies to all structures. Power to a building has to be disconnected with no more then six motions of the hand. It has nothing to do with subpanels or devices.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
The Following 2 Users Say Thank You to electures For This Useful Post:
Code05 (08-16-2011), dimyself121 (08-16-2011)
Old 08-16-2011, 12:00 PM   #29
Code05's Avatar
Huh?
Old 08-16-2011, 12:20 PM   #30
Electures clarified what I was meaning.
Multiple Panel Question theatretch85 Electrical 7 09-29-2016 08:15 PM
More Sub Panel Questions rdkng07 Electrical 6 05-25-2011 09:46 AM
New Breaker Panel Questions AvalonGirl Electrical 10 06-02-2010 11:20 AM
Service panel and general questions reddman Electrical 3 05-12-2009 12:54 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 08:37 AM