i decided to post these questions under a new topic since they dont pertain to my original question...i recently had my electrical service upgraded and due to a continued lack of breaker positions i plan on using my old smaller breaker box as a subpanel. i will use a 40 or 50 amp 2 pole breaker in the new box to feed the subpanel. pls refer to my pictures of the subpanel. i dont appear to have the lugs on the top of the panel to bring my feed wires to. should i just put my two hot wires to the left side of the 100 amp double pole breaker , making that be my main? also it is suggested i bring The ground (bare) wire to the ground bus. i dont appear to have a seperate ground bus in this panel ,can i hook the bare wire to the neutral bus bar with the white wire or should a i buy a ground bar and install it for the bare wire?
pberm1962 is offline   Reply With Quote
Old 10-02-2011, 02:39 PM   #2
I=E/R
a7ecorsair's Avatar
Yes It will be treated as a disconnect
also it is suggested i bring The ground (bare) wire to the ground bus. i dont appear to have a seperate ground bus in this panel ,can i hook the bare wire to the neutral bus bar with the white wire NO or should a i buy a ground bar and install it for the bare wire?
You will need a separate ground bus. This bus will be fastened to the panel case and you will have to remove any bonding that is present between the neutral bar and the case.
I added answer above
Wait, I went back and looked at the pictures. Do I see two bars at the bottom of the panel?
a7ecorsair is offline   Reply With Quote
Old 10-02-2011, 02:47 PM   #3
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,192
You can back feed the 100 amp breaker and it will serve as a disconnect. That will require a hold down kit for the 100 amp breaker.
40 amp breaker in the main panel will need 8/3 cable to the sub, 50 amp will require 6/3 (I would go 50 amp with 6/3).
You will need to add a separate ground bar ion the sub and separate the grounds and neutrals.
Coastal South Carolina
rjniles is offline   Reply With Quote
Old 10-02-2011, 02:51 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,950
That is an original main breaker panel. The breaker will already have a hold down.
Old 10-02-2011, 02:52 PM   #5
Licensed electrician
Rewards Points: 1,506
That 100 was a main and probably does not need the hold down. It is not being backfeed. It was the design that style used.
Old 10-02-2011, 03:34 PM   #6
Rewards Points: 31
more questions
a7 yes there are two bars at the bottom of the panel but they are both connected to the neutral bar. i see that i will have to add a seperate ground bar and seperate the ground and neutral wires... a7ecorsair.... you mentioned that i will have to remove any bonding that is present between the neutral bar and the case. how do i go about that?
Panel cleanup gdoucette Electrical 5 06-26-2010 02:01 PM
Extending Old Main Circuit Panel lkpowell Electrical 4 10-23-2008 02:15 PM
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 10:27 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 07:37 AM