Sub-panel Grounding Question. - Electrical - Page 3 - DIY Chatroom Home Improvement Forum
Old 02-22-2008, 07:51 AM   #31
250.32 (A) exception. With a 4 wire system the pannel at the garage doesn't need to be grounded. In a 4 wire isolated ground system if you put a ground on the pannel you will fail inspection. NEC 2005 page 70-99. I understood it to be a "detatched garage". I just pointed out that you go by code, and don't just throw a ground in when ever you want.
RobertS is offline   Reply With Quote
Old 02-22-2008, 08:25 AM   #32
Licensed Pro
230.32 (A) exception. With a 4 wire system the pannel at the garage doesn't need to be grounded. In a 4 wire isolated ground system if you put a ground on the pannel you will fail inspection. NEC 2005 page 70-99.
I believe you mean 250.32(A). And the exception applies only when a single branch circuit (or MWBC) is run to the separate building. If you run a subpanel in the detached building with either 3 wires or 4, a grounding electrode is required.