Sub Panel Grounding Bar - Electrical - DIY Chatroom Home Improvement Forum
Old 05-23-2009, 02:47 PM   #1
Sub Panel Grounding bar
Are the grounding wires and the neutral wires connected to the same bar in a sub panel?
bmancanfly is offline   Reply With Quote
Old 05-23-2009, 02:51 PM   #2
Rewards Points: 29
No you need a separate ground bar.
jsmith929 is offline   Reply With Quote
Old 05-23-2009, 03:02 PM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,992
It's that easy.
True, with most installations the grounds and neutrals are kept separate, but in some cases a sub-panel in a detached structure have the neutrals and grounds bonded.
Old 05-23-2009, 03:31 PM   #4
thanks guys. I thought that was the case. But I looked in my detached cottage behind my house and it has the neutral and ground wires on the same bar. But I think that's the only situation where it is allowed - a detached structure.
Old 05-23-2009, 03:36 PM   #5
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Only if there are no other metallic paths between the structure with the service equipment and the detached structure (like a metal water pipe or data/phone lines) and only if your area is on a code cycle prior to 2008.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 05-23-2009, 05:45 PM   #6
Rewards Points: 29
I was assuming same structure and with a ground to the sub (my bad on the assuming part)
Old 05-23-2009, 09:30 PM   #7
Yup. That's the "some cases" I was talking about.
Old 05-23-2009, 09:38 PM   #8
Originally Posted by fast1 View Post
yea agreed. you got it spot on...
The Red X strikes again
Does anyone see a pic, or just the RED X ???
Old 05-23-2009, 11:55 PM   #9
if ground and Neutral should be on same bar in subpnl.
It's not to be taken lightly. (separation of ground and neutral conductors in subpanel)! I've seen subpanels where the ground and neutral conductors were not separated, especially on non-linear loads, like computers and electronic copiers that the panel and breakers were hot to the touch and there was vibration, like a hum or buzzzzzzzzzzz...!
spark plug is offline   Reply With Quote
Old 05-24-2009, 07:30 AM   #10
Spark, did you even read any of the other replies? Are you familiar with NEC 250.32(B)?
I for one sure would like an explanation of how this has anything to do with having the ground and neutral on the same bar in cases where the neutral is also used as the grounding conductor.
Old 05-24-2009, 07:50 AM   #11
Bigplanz's Avatar
Rewards Points: 996
I can only offer what I have read about this subject. I have read that the ground and neutral can only be bonded at the main panel and nowhere else. I have also read differing views on grounding a subpanel. What I have read is that if the conduit is all metal (continuous grounding path or a separate ground wire is run from the main panel to the subpanel ground bar, then that is acceptable. Also, a separate grounding electrode for the subpanel is acceptable. In no instance, however, are the neutral and ground ever bonded together except at the main panel.
If this is incorrect, I am sure someone will point it out. A quick search of the Internet revealed this interesting document concerning grounding a subpanel.
http://www.co.shasta.ca.us/Departmen...Structures.pdf
Bigplanz is offline   Reply With Quote
Old 05-24-2009, 10:29 AM   #12
Well, some is true, some is hearsay, some is a vague generalization. I'll admit, this is typical information you might find on the interweb.
The NEC (or local codes) are the ONLY reading that really matter.
Not true.
Yes, a metallic conduit system is an acceptable grounding conductor.
A grounding electrode is NOT at all related to the equipment ground run with a feeder or branch circuit. A grounding electrode will NEVER replace or substitute an equipment ground.
However, a grounding electrode is ALWAYS required for a detached structure with a feeder and sub-panel, but it serves a very different purpose than the equipment ground. Confusing as that is.
Wrong. See NEC 250.32(B) as referenced above.
Here, I will give you the section. Keep in mind, this is from the 2008 NEC. Prior to this there was no "exception" to (B) below. It was expressly allowed in prior versions. This was changed in 2008 and made into the exception you see below.
250.32 Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s).
(B) Grounded Systems.
For a grounded system at the separate building or structure, an equipment grounding conductor as described in 250.118 shall be run with the supply conductors and be connected to the building or structure disconnecting means and to the grounding electrode(s). The equipment grounding conductor shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. The equipment grounding conductor shall be sized in accordance with 250.122. Any installed grounded conductor shall not be connected to the equipment grounding conductor or to the grounding electrode(s).
Exception: For existing premises wiring systems only, the grounded conductor run with the supply to the building or structure shall be permitted to be connected to the building or structure disconnecting means and to the grounding electrode(s) and shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded where all the requirements of (1), (2), and (3) are met:
(1) An equipment grounding conductor is not run with the supply to the building or structure.
(2) There are no continuous metallic paths bonded to the grounding system in each building or structure involved.
(3) Ground-fault protection of equipment has not been installed on the supply side of the feeder(s).
For clarity, the grounded conductor is the neutral and the grounding conductor is the equipment ground.
Old 05-24-2009, 02:07 PM   #13
Bigplanz's Avatar
Rewards Points: 996
Not true.
Thanks again for your detailed answer. To make things even more confusing, local jurisdictions have their own 'home rules' that may not be in the NEC at all. Louisville, I am discovering, has several such local rules. I suppose the requirements from Shasta, CA are also their 'local rules.'
Detached Garage Sub Panel Grounding Q integlikewhoa Electrical 15 03-12-2015 07:02 PM
sub panel grounding jprince Electrical 2 05-04-2009 06:15 PM
new Main Panel Grounding lrr81765 Electrical 8 10-09-2008 11:16 AM
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 10:27 AM
advice on installing equipment grounding bar in main panel pacifier1er Electrical 5 05-29-2007 05:55 PM