Sub Panel In Garage Question ( Grounding) - Electrical - DIY Chatroom Home Improvement Forum
Old 11-20-2012, 11:25 AM   #1
sub panel in garage question ( grounding)
Hello
I am installing a new sub panel in my garage.
I am running 6-3 tech wire to the panel from my 100 amp panel in the house.
The sub panel will be on a 50 amp breaker.
I understand that I need some form of grounding for the panel at the garage.
Can I use a grounding plate or do I have to use grounding rods?
How deep does the plate need to go?
onebladerz is offline   Reply With Quote
Old 11-20-2012, 11:28 AM   #2
Rewards Points: 82
If the garage is attached to the house, you need only an EGC. If the garage is not attached to the house, you need the EGC and ground rods. So what you got? Attached or unattached?
Whats tech wire?
Old 11-20-2012, 11:35 AM   #3
Teck wire is armored exterior direct burial wire.
What is the EGC?
Old 11-20-2012, 11:37 AM   #4
Rewards Points: 324
EGC = equipment grounding conductor.
oleguy74 is offline   Reply With Quote
Old 11-20-2012, 11:39 AM   #5
JOATMON
ddawg16's Avatar
Rewards Points: 1,154
Earth Ground Connection....
Basically.....you sink 2 ground rods at the grarge....6-8' feet apart....you connect that ground to the ground buss in your sub panel. You ALSO connect the ground from your load center to the ground buss.
You do NOT connect the neutral and ground together in the sub.....
If your sub is like most....you will need to pick up ground buss to install in the sub.
Plate? Haven't heard that one......unless your talking about an Ufer ground....
Do the rods....keep it simple.
ddawg16 is online now   Reply With Quote
Old 11-20-2012, 11:59 AM   #6
Licensed electrician
Rewards Points: 1,272
Sounds like the OP is in Canada.
Old 11-20-2012, 12:00 PM   #7
Rewards Points: 324
ground plates were used for years.just a flat ground rod.telco's used huge copper plates for CO grounds.ours were like a 4x8 copper sheets 1/2 to 3/4" thick.they are buried instead of driven in.nec ref 250.56.250.52(A)(6).250.53(h).
Old 11-20-2012, 12:42 PM   #8
Rewards Points: 776
Well a 4' x 8' x 1/2" sheet of copper will cost you about $2,604 at today's copper spot rate. Maybe the ground rods would be a tad bit cheaper......
curiousB is offline   Reply With Quote
Old 11-20-2012, 01:13 PM   #9
Rewards Points: 324
that is for office ground.they can be copper plated but yes a ground rod is ok.that was an example for d dwagg as he seemed not familler with plates.you can get copper-weld plates just like ground rods.
Garage Sub Panel curiousB Electrical 18 08-16-2012 06:42 PM
Sub Panel GND and mixed 240/120 VAC branch curiousB Electrical 12 01-17-2012 11:49 AM
Yet another sub panel question jboggz Electrical 4 06-19-2011 09:27 PM
Garage slab pour, Control joint and grounding question italie Building & Construction 0 05-17-2011 11:02 AM
Next Question, Sub panel in detached garage... OmegaBunny Electrical 5 09-16-2008 12:37 AM