rtyui2 11-28-2007 08:59 AM
I am just completing a large remodel and have added 2 bathrooms, 2 bedrooms, and a space for a washer and dryer upstairs. Instead of running all the wires two stories down to the basement where the main panel is, I installed a 100 amp subpanel in the new upstairs. The sub panel has a main breaker. I have three questions. Do I run a ground wire from the sub panel all the way down to the main service panel ground connection (that is, the re-bar extending out of the new foundation wall next to the service panel)? What wire do I use to connect the service and sub panels, and, this is a separate question....................how many outlets should be installed in a typical bedroom. Thanks
Mike
HouseHelper 11-28-2007 09:16 AM
The subpanel should be fed by 4 wires: 2 hot, 1 neutral, 1 ground. It is not necessary to provide a 100A feed just because it is a 100A panel, in your case a 60A feed would be sufficient. You could then use 6/3 w/G cable to feed the subpanel.
The number of receptacles (I assume that is what you mean be outlets) in a bedroom is up to you, as long as you meet the minimum requirements of no point in any wall space being more than 6' from a receptacle and a receptacle in any wall space 2' or more in width.
And AFCI protection of the bedroom receptacles AND lights AND smoke detectors (unless local amendments except these).
EDIT to add: In most bedrooms I do, I have a minimum of 7 receptacles. Some master BRs may have twice that. I also try to work with the owner to determine bed placement so there is not a receptacle directly behind the bed.
ponch37300 11-28-2007 09:18 AM
Mike, there is another thread abuot a 100 amp sub panel from yesterday that may or may not help you, just scroll down the electrical section and you will see it. As far as the outlets it's not the number but the placement that determins how many you end up with. I believe(hopefully someone will be along to confirm or correct this) It's one outlet within six feet or an opening(door or closet door) and 12 feet inbetween the next ones. So measure six feet from your door and you need one within that six ft, that is the max, then measure 12 ft from that outlet and you need one within that twelve ft.
J. V. 11-28-2007 10:57 AM
HouseHelper is correct. But make sure you do not connect the neutrals and grounds (EGC's) together in the sub panel. They must be seperated. If this is a new panel, you most likely have two terminal strips running vertically along the inside of the sub panel. There may be a bar that connects both terminal strips. Remove the bar and use one strip neutrals and the other for the grounds.
I agree you do not need a 100 amp panel for this application.
rtyui2 11-28-2007 01:15 PM
thanks for the help
Stubbie 11-28-2007 03:29 PM
To clarify one of your questions...... You asked if you run a ground wire down to the rebar (ufer electrode). No you do not. You only do this from your main panel.
As for removing the bonding strap between neutral bars... this by itself will not make one bar a ground bar. And in some this strap is not removable, and you must use a ground bar kit.....so use caution. In all split neutrals both bars are on insulated standoffs.
When you remove that strap you must be sure that you have the bar you want as the ground bar...which will be the one the service neutral isn't connected to... bonded to the metal of the panel. You do this with a bonding jumper like this.....also if a bonding jumper or bonding means is installed on the same bar as the service neutral you must remove it.
http://www.hammerzone.com/archives/e.../elspra11a.jpg
chris75 11-28-2007 04:24 PM
1 Attachment(s)
Attachment 1761
Here is what is required...